    freezing suction line



    have a carrier roof top suction presuuer fine and head pressure fine airflow good to suction line out of evap frost back within two mins of running



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: freezing suction line

    Hi :
    what ***** are u using ?
    what are the pressures?
    superheat?
    subcooling?
    some info could help!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  3. #3
    Join Date
    Feb 2010
    Location
    NT
    Posts
    66
    Rep Power
    15

    Re: freezing suction line

    If the system is using TXV or EEV check the subcooling if its using fix bore metering check the superheat.This two information tells it all.

  4. #4
    Join Date
    Apr 2005
    Location
    INDIA
    Age
    63
    Posts
    84
    Rep Power
    20

    Re: freezing suction line

    Less air flow in evp or excess gas.

    Regds

  5. #5
    Join Date
    May 2010
    Location
    United States
    Posts
    47
    Rep Power
    0

    Re: freezing suction line

    Quote Originally Posted by hodgy911 View Post
    have a carrier roof top suction presuuer fine and head pressure fine airflow good to suction line out of evap frost back within two mins of running
    If it's frosting back, then then the suction pressure isn't fine. Frosting back within two minutes would also pretty much require low superheat. If airflow seemed fine, then you should check it again, because it may not be fine. Also look for a restriction of one or more of the orifices.

  6. #6
    Join Date
    Jun 2007
    Location
    darwin
    Age
    46
    Posts
    13
    Rep Power
    0

    Re: freezing suction line

    Is the indoor fan belt driven.

  7. #7
    Join Date
    May 2010
    Location
    ipswich
    Age
    32
    Posts
    26
    Rep Power
    0

    Re: freezing suction line

    Was it a humid day? All I can think of is frost lines... dont worry about them. they do not gauge anything no matter how serious they look

  8. #8
    Join Date
    Jul 2010
    Location
    England
    Age
    64
    Posts
    8
    Rep Power
    0

    Re: freezing suction line

    Does it stay frosted, all the time the compressor is running?

  9. #9
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: freezing suction line

    Definately need more info.
    Like said before above I would check superheat.
    Need to know if it flooding back or Frosting.
    Best way I describe this to apprentices that annoy me is.

    Stick your tounge on the suction pipe. If you can get it off then its frosting back. If you cant then it is flooding back.

    Frosting -Low gas / Restriction metering device.

    Flooding Back -Low Air flow /overcharge/ Metering device problem.

    Biggest problem with package unit is airflow. Need to adjust pullys based on duct static and rated airflow.
    No longer Active

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: freezing suction line

    Frosting of the suction line can also be attributed to a low indoor heat source on an A/C install

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. suction line velocity
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 16
    Last Post: 24-08-2008, 01:26 PM
  4. Suction Line Freezing
    By John Kuchinic in forum Fundamentals
    Replies: 39
    Last Post: 12-02-2008, 01:48 AM
  5. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •