15-06-2010, 02:10 AM #1
freezing suction line
have a carrier roof top suction presuuer fine and head pressure fine airflow good to suction line out of evap frost back within two mins of running
-
15-06-2010, 04:51 AM #2
Re: freezing suction line
Hi :
what ***** are u using ?
what are the pressures?
superheat?
subcooling?
some info could help!THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
15-06-2010, 12:40 PM #3
Re: freezing suction line
If the system is using TXV or EEV check the subcooling if its using fix bore metering check the superheat.This two information tells it all.
-
19-06-2010, 06:57 PM #4
Re: freezing suction line
Less air flow in evp or excess gas.
Regds
-
20-06-2010, 04:06 AM #5
Re: freezing suction line
If it's frosting back, then then the suction pressure isn't fine. Frosting back within two minutes would also pretty much require low superheat. If airflow seemed fine, then you should check it again, because it may not be fine. Also look for a restriction of one or more of the orifices.
-
20-06-2010, 05:53 AM #6
Re: freezing suction line
Is the indoor fan belt driven.
-
16-07-2010, 09:00 AM #7
Re: freezing suction line
Was it a humid day? All I can think of is frost lines... dont worry about them. they do not gauge anything no matter how serious they look
-
16-07-2010, 10:58 AM #8
Re: freezing suction line
Does it stay frosted, all the time the compressor is running?
-
16-07-2010, 11:36 AM #9
Re: freezing suction line
Definately need more info.
Like said before above I would check superheat.
Need to know if it flooding back or Frosting.
Best way I describe this to apprentices that annoy me is.
Stick your tounge on the suction pipe. If you can get it off then its frosting back. If you cant then it is flooding back.
Frosting -Low gas / Restriction metering device.
Flooding Back -Low Air flow /overcharge/ Metering device problem.
Biggest problem with package unit is airflow. Need to adjust pullys based on duct static and rated airflow.No longer Active
-
16-07-2010, 06:59 PM #10
Re: freezing suction line
Frosting of the suction line can also be attributed to a low indoor heat source on an A/C install
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Some information on the aplication of suction gas/liquid line heat exchangers
By SteinarN in forum FundamentalsReplies: 5Last Post: 14-09-2009, 07:33 AM -
suction line velocity
By Kevin Yeo in forum Supermarket RefrigerationReplies: 16Last Post: 24-08-2008, 01:26 PM -
Suction Line Freezing
By John Kuchinic in forum FundamentalsReplies: 39Last Post: 12-02-2008, 01:48 AM -
Benji
By benji in forum Trouble ShootingReplies: 29Last Post: 30-01-2008, 01:25 PM