Results 1 to 19 of 19
Thread: A/c unit not cooling
-
14-06-2010, 11:37 PM #1
A/c unit not cooling
Hey, I need some help on this one. I have a 2.5 ton unit with condensor unit working and an air handler that the unit is working. Everything runs. Pressure is at 70 low and 195 high. I get no condensation on the low side line and a faint warmness on the high side line. Thermostat is set at 73 and room temp is reading 80 deg. I put a thermometer in the vent and the cool air coming out is 70 deg. The apartment is not cooling down. I added some ***** to the system to get up to 100 psi on the low side and this had the low side line sweating with condensate, but i know it is not healthy to have that high a press reading. Coils are clean, filter is new. Any suggesstions would be great. If you need any other info please let me know.
-
14-06-2010, 11:52 PM #2
Re: A/c unit not cooling
Any idea what the gas is? 'cos we haven't.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
15-06-2010, 02:10 AM #3
-
15-06-2010, 04:49 AM #4
Re: A/c unit not cooling
THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
15-06-2010, 12:14 PM #5
Re: A/c unit not cooling
How do I tell if there is a restriction? I will try to evac today and recharge system
-
23-06-2010, 01:06 AM #6
Re: A/c unit not cooling
I'm a new member so, sorry to jump your post Johnny, but this looked like the place to start. I'm supposed to know this stuff but am having a similar problem with my own unit. Just replaced 2.0 ton 10 SEER evap and condenser R-22 with 2.0 ton 13 SEER R-22 condenser and coil (matched set). Filter is clean. New dryer on liquid side near evap coil. Used the orifice that came with new unit (size was correct per chart). Line set is about 30 feet - didnot add refrigerant to the factory charge. Now I'm only getting 17.5 degrees drop across the coil (at the coil). With unit at steady state running for over an hour: 89 degree ambient, 102 condenser discharge temp, 61% humidity, 75 degree interior (no hum check), 205 psi liquid line, 75 psi suction line, liquid line temp 88-89, Superheat appears to be 16 degrees, RAT at coil - 78.5 (attic unit - must assume some leaky ductwork - 1990 install date), SAT at coil 61.0. This thing is whupping my tail. The system was only open to atmosphere for about an hour. I pulled a deep vaccume and held it for several hours. Charged with dry nitrogen - to 250 - watched for an hour - no drop. What am I missing? Is the orifice too large? My high side appears low. But the low side looks high. To me that says I'm flowing too much refrigerant through the evap. If so, what size should the orifice be?
-
23-06-2010, 06:55 AM #7
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: A/c unit not cooling
Restriction could be spotted where temperature of line before and after restriction is different more than 1°F.
For proper evaluation we need this readings:
Evap air/water in temp
Evap air/water out temp
Low side pressure or saturation temp
Suction line temp at evap outlet
Suction line temp at compressor inlet
Cond air/water in temp
Cond air/water out temp
High side pressure or saturation temp
Liquid line temp at receiver or condenser outlet
Liquid line temp at TXV/ inlet
The more information provided the more accurate the diagnosis.
-
23-06-2010, 07:19 AM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: A/c unit not cooling
Higher SEER mean lower coil dT. That also mean little higher evaporation and little lower condensation than on 10 SEER coils.
Superheat is 8K (16°F) which look OK to me for your conditions, if we presume that indoor humidity is also near 60% (Indoor WB 65°F) .
You can evaluate your system by measuring air flow across evaporator and by measuring air temperature and humidity before and after coil.
If you have correct airflow of 800 FPM and about 3 l/h condensate, your evaporator coil achieves 2 Ton of duty with that dT.Last edited by nike123; 23-06-2010 at 07:37 AM.
-
24-06-2010, 03:19 AM #9
Re: A/c unit not cooling
Wow, thanks for the quick response. I measured via aneometer (sic) fpm at each supply, totaled and divided by # of supply's x sq ft id of the coil box and got 720 cfm - given leakage and the error factor the actual cfm is at least 800 cfm.
I didn't check the orifice but it must be right - they would not ship anything much larger than a 063 for 24,000 Btu. I suppose I'll check that eventually.
Maybe i'm just not going to see more than 17 or 18 dT at the coil on this 13 seer unit.
Relative humidty was about 55%.
Next time I get worked up, I'll check the orifice size.
Thanks again!
-
26-06-2010, 01:56 PM #10
-
01-02-2011, 02:57 PM #11
Re: A/c unit not cooling
you sytem is have a air lock, check you cooling tower water..
-
01-02-2011, 04:28 PM #12
Re: A/c unit not cooling
Assuming all else is working properly, the dT is a function of airflow. Lowering the airflow raises the dT. Raising the airflow lowers the dT.
If you want to get the dT up to 20F, lower the fan speed... but keep in mind that lower fan speed (higher dT) decreases your efficiency, while higher fan speed (lower dT) removes less humidity from the air. If you are happy with the humidity level, you may want to leave it as is.Last edited by Gary; 01-02-2011 at 04:38 PM.
-
01-02-2011, 05:00 PM #13
Re: A/c unit not cooling
The air temp at the vent just won't do. We need to know the air temps, in and out, as close to the air handler (AHU) as possible. Usually on a ducted system there is a flexible duct connector at the AHU and this provides a handy place to poke a tiny hole and insert your thermometer.
Adding refrigerant was a big mistake.
-
01-02-2011, 05:29 PM #14
Re: A/c unit not cooling
Hi
look at the dates!THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
01-02-2011, 05:47 PM #15
Re: A/c unit not cooling
Late to the party again... story of my life... lol
-
01-02-2011, 06:49 PM #16
Re: A/c unit not cooling
Hi
it seems like this guy was on a writing frenzy,never seen anybody answer 14 old threads on one shot ,and it is never to late to party so bring the beer on !
take care garyTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
01-02-2011, 08:42 PM #17
-
01-02-2011, 08:54 PM #18
Re: A/c unit not cooling
I watched a TV show recently called "How beer saved the world". Interesting stuff. Turns out beer is what began civilization by starting agriculture. The first known crop was barley, which everyone assumed was used to make bread, but in fact it was cultivated 300 years before bread was invented and examination of pottery used in that area during that time period showed barley/beer residue. They were using the barley to make beer.
The show went on to very plausibly demonstrate how a long list of advances in human development were directly or indirectly brought about by the quest for beer, from the building of the pyramids to the discovery of germs/pastuerization to the beginnings of automation and the elimination of child labor.Last edited by Gary; 01-02-2011 at 09:10 PM.
-
01-02-2011, 08:59 PM #19
Re: A/c unit not cooling
HI
now we know it really isnt never to late to party,what a choice bread or beer????THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
Similar Threads
-
Daikin VRV vs. Mitsubishi Multi City
By Gabriel Gagnon in forum Technical DiscussionsReplies: 19Last Post: 15-02-2011, 06:12 PM -
Split board consumer unit
By Swipe in forum Air ConditioningReplies: 34Last Post: 07-05-2009, 07:11 PM -
DIAGRAMS : Cooling Discharge/Suction pressure vs. Outdoor temp
By psalom in forum DomesticReplies: 0Last Post: 28-08-2007, 09:48 AM -
hitachi utopia g7 r404a not up to cooling
By peter1927 in forum Trouble ShootingReplies: 12Last Post: 16-01-2006, 03:19 AM -
Regulation of cooling capacity
By npaisnel in forum DomesticReplies: 13Last Post: 08-02-2002, 11:22 PM