    Question A/c unit not cooling



    Hey, I need some help on this one. I have a 2.5 ton unit with condensor unit working and an air handler that the unit is working. Everything runs. Pressure is at 70 low and 195 high. I get no condensation on the low side line and a faint warmness on the high side line. Thermostat is set at 73 and room temp is reading 80 deg. I put a thermometer in the vent and the cool air coming out is 70 deg. The apartment is not cooling down. I added some ***** to the system to get up to 100 psi on the low side and this had the low side line sweating with condensate, but i know it is not healthy to have that high a press reading. Coils are clean, filter is new. Any suggesstions would be great. If you need any other info please let me know.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: A/c unit not cooling

    Any idea what the gas is? 'cos we haven't.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    johnnyirish11's Avatar
    johnnyirish11 Guest

    Re: A/c unit not cooling

    Quote Originally Posted by Brian_UK View Post
    Any idea what the gas is? 'cos we haven't.



    Yes sorry unit is R 22

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: A/c unit not cooling

    Quote Originally Posted by johnnyirish11 View Post
    Yes sorry unit is R 22
    Hi:
    your high side is low, should be at aprox - 220-250 psi ,you should have some sort of pressure control,by adding too much refrigerant you probably floded the condenser,evacuate the sys and charge by wheight or pressure correctly .
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  5. #5
    johnnyirish11's Avatar
    johnnyirish11 Guest

    Re: A/c unit not cooling

    How do I tell if there is a restriction? I will try to evac today and recharge system

  6. #6
    Pilotman's Avatar
    Pilotman Guest

    Re: A/c unit not cooling

    I'm a new member so, sorry to jump your post Johnny, but this looked like the place to start. I'm supposed to know this stuff but am having a similar problem with my own unit. Just replaced 2.0 ton 10 SEER evap and condenser R-22 with 2.0 ton 13 SEER R-22 condenser and coil (matched set). Filter is clean. New dryer on liquid side near evap coil. Used the orifice that came with new unit (size was correct per chart). Line set is about 30 feet - didnot add refrigerant to the factory charge. Now I'm only getting 17.5 degrees drop across the coil (at the coil). With unit at steady state running for over an hour: 89 degree ambient, 102 condenser discharge temp, 61% humidity, 75 degree interior (no hum check), 205 psi liquid line, 75 psi suction line, liquid line temp 88-89, Superheat appears to be 16 degrees, RAT at coil - 78.5 (attic unit - must assume some leaky ductwork - 1990 install date), SAT at coil 61.0. This thing is whupping my tail. The system was only open to atmosphere for about an hour. I pulled a deep vaccume and held it for several hours. Charged with dry nitrogen - to 250 - watched for an hour - no drop. What am I missing? Is the orifice too large? My high side appears low. But the low side looks high. To me that says I'm flowing too much refrigerant through the evap. If so, what size should the orifice be?

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: A/c unit not cooling

    Quote Originally Posted by johnnyirish11 View Post
    How do I tell if there is a restriction? I will try to evac today and recharge system
    Restriction could be spotted where temperature of line before and after restriction is different more than 1°F.

    For proper evaluation we need this readings:

    Evap air/water in temp
    Evap air/water out temp
    Low side pressure or saturation temp
    Suction line temp at evap outlet
    Suction line temp at compressor inlet

    Cond air/water in temp
    Cond air/water out temp
    High side pressure or saturation temp
    Liquid line temp at receiver or condenser outlet
    Liquid line temp at TXV/ inlet




    The more information provided the more accurate the diagnosis.

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: A/c unit not cooling

    Quote Originally Posted by Pilotman View Post
    I'm a new member so, sorry to jump your post Johnny, but this looked like the place to start. I'm supposed to know this stuff but am having a similar problem with my own unit. Just replaced 2.0 ton 10 SEER evap and condenser R-22 with 2.0 ton 13 SEER R-22 condenser and coil (matched set). Filter is clean. New dryer on liquid side near evap coil. Used the orifice that came with new unit (size was correct per chart). Line set is about 30 feet - didnot add refrigerant to the factory charge. Now I'm only getting 17.5 degrees drop across the coil (at the coil). With unit at steady state running for over an hour: 89 degree ambient, 102 condenser discharge temp, 61% humidity, 75 degree interior (no hum check), 205 psi liquid line, 75 psi suction line, liquid line temp 88-89, Superheat appears to be 16 degrees, RAT at coil - 78.5 (attic unit - must assume some leaky ductwork - 1990 install date), SAT at coil 61.0. This thing is whupping my tail. The system was only open to atmosphere for about an hour. I pulled a deep vaccume and held it for several hours. Charged with dry nitrogen - to 250 - watched for an hour - no drop. What am I missing? Is the orifice too large? My high side appears low. But the low side looks high. To me that says I'm flowing too much refrigerant through the evap. If so, what size should the orifice be?

    Higher SEER mean lower coil dT. That also mean little higher evaporation and little lower condensation than on 10 SEER coils.
    Superheat is 8K (16°F) which look OK to me for your conditions, if we presume that indoor humidity is also near 60% (Indoor WB 65°F) .
    You can evaluate your system by measuring air flow across evaporator and by measuring air temperature and humidity before and after coil.

    If you have correct airflow of 800 FPM and about 3 l/h condensate, your evaporator coil achieves 2 Ton of duty with that dT.
    Last edited by nike123; 23-06-2010 at 07:37 AM.

  9. #9
    Pilotman's Avatar
    Pilotman Guest

    Re: A/c unit not cooling

    Wow, thanks for the quick response. I measured via aneometer (sic) fpm at each supply, totaled and divided by # of supply's x sq ft id of the coil box and got 720 cfm - given leakage and the error factor the actual cfm is at least 800 cfm.

    I didn't check the orifice but it must be right - they would not ship anything much larger than a 063 for 24,000 Btu. I suppose I'll check that eventually.

    Maybe i'm just not going to see more than 17 or 18 dT at the coil on this 13 seer unit.

    Relative humidty was about 55%.

    Next time I get worked up, I'll check the orifice size.

    Thanks again!

  10. #10
    Join Date
    May 2010
    Location
    United States
    Posts
    47
    Rep Power
    0

    Re: A/c unit not cooling

    Quote Originally Posted by johnnyirish11 View Post
    Hey, I need some help on this one. I have a 2.5 ton unit with condensor unit working and an air handler that the unit is working. Everything runs. Pressure is at 70 low and 195 high. I get no condensation on the low side line and a faint warmness on the high side line. Thermostat is set at 73 and room temp is reading 80 deg. I put a thermometer in the vent and the cool air coming out is 70 deg. The apartment is not cooling down. I added some ***** to the system to get up to 100 psi on the low side and this had the low side line sweating with condensate, but i know it is not healthy to have that high a press reading. Coils are clean, filter is new. Any suggesstions would be great. If you need any other info please let me know.
    Why don't you just call a pro? At this rate you'll be replacing a compressor soon.

  11. #11
    Join Date
    Feb 2011
    Location
    malaysia
    Posts
    5
    Rep Power
    0

    Re: A/c unit not cooling

    you sytem is have a air lock, check you cooling tower water..

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: A/c unit not cooling

    Quote Originally Posted by Pilotman View Post
    Wow, thanks for the quick response. I measured via aneometer (sic) fpm at each supply, totaled and divided by # of supply's x sq ft id of the coil box and got 720 cfm - given leakage and the error factor the actual cfm is at least 800 cfm.

    I didn't check the orifice but it must be right - they would not ship anything much larger than a 063 for 24,000 Btu. I suppose I'll check that eventually.

    Maybe i'm just not going to see more than 17 or 18 dT at the coil on this 13 seer unit.

    Relative humidty was about 55%.

    Next time I get worked up, I'll check the orifice size.

    Thanks again!
    Assuming all else is working properly, the dT is a function of airflow. Lowering the airflow raises the dT. Raising the airflow lowers the dT.

    If you want to get the dT up to 20F, lower the fan speed... but keep in mind that lower fan speed (higher dT) decreases your efficiency, while higher fan speed (lower dT) removes less humidity from the air. If you are happy with the humidity level, you may want to leave it as is.
    Last edited by Gary; 01-02-2011 at 04:38 PM.

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: A/c unit not cooling

    Quote Originally Posted by johnnyirish11 View Post
    Hey, I need some help on this one. I have a 2.5 ton unit with condensor unit working and an air handler that the unit is working. Everything runs. Pressure is at 70 low and 195 high. I get no condensation on the low side line and a faint warmness on the high side line. Thermostat is set at 73 and room temp is reading 80 deg. I put a thermometer in the vent and the cool air coming out is 70 deg. The apartment is not cooling down. I added some ***** to the system to get up to 100 psi on the low side and this had the low side line sweating with condensate, but i know it is not healthy to have that high a press reading. Coils are clean, filter is new. Any suggesstions would be great. If you need any other info please let me know.
    The air temp at the vent just won't do. We need to know the air temps, in and out, as close to the air handler (AHU) as possible. Usually on a ducted system there is a flexible duct connector at the AHU and this provides a handy place to poke a tiny hole and insert your thermometer.

    Adding refrigerant was a big mistake.

  14. #14
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: A/c unit not cooling

    Hi
    look at the dates!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  15. #15
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: A/c unit not cooling

    Late to the party again... story of my life... lol

  16. #16
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: A/c unit not cooling

    Hi
    it seems like this guy was on a writing frenzy,never seen anybody answer 14 old threads on one shot ,and it is never to late to party so bring the beer on !
    take care gary
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  17. #17
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: A/c unit not cooling

    Quote Originally Posted by goshen View Post
    Hi
    it seems like this guy was on a writing frenzy,never seen anybody answer 14 old threads on one shot ,and it is never to late to party so bring the beer on !
    take care gary
    Just waiting for the eventual URL Link or similar post once he reaches 15 posts.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  18. #18
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: A/c unit not cooling

    Quote Originally Posted by goshen View Post
    Hi
    it seems like this guy was on a writing frenzy,never seen anybody answer 14 old threads on one shot ,and it is never to late to party so bring the beer on !
    take care gary
    I watched a TV show recently called "How beer saved the world". Interesting stuff. Turns out beer is what began civilization by starting agriculture. The first known crop was barley, which everyone assumed was used to make bread, but in fact it was cultivated 300 years before bread was invented and examination of pottery used in that area during that time period showed barley/beer residue. They were using the barley to make beer.

    The show went on to very plausibly demonstrate how a long list of advances in human development were directly or indirectly brought about by the quest for beer, from the building of the pyramids to the discovery of germs/pastuerization to the beginnings of automation and the elimination of child labor.
    Last edited by Gary; 01-02-2011 at 09:10 PM.

  19. #19
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: A/c unit not cooling

    HI
    now we know it really isnt never to late to party,what a choice bread or beer????
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. Daikin VRV vs. Mitsubishi Multi City
    By Gabriel Gagnon in forum Technical Discussions
    Replies: 19
    Last Post: 15-02-2011, 06:12 PM
  2. Split board consumer unit
    By Swipe in forum Air Conditioning
    Replies: 34
    Last Post: 07-05-2009, 07:11 PM
  3. Replies: 0
    Last Post: 28-08-2007, 09:48 AM
  4. hitachi utopia g7 r404a not up to cooling
    By peter1927 in forum Trouble Shooting
    Replies: 12
    Last Post: 16-01-2006, 03:19 AM
  5. Regulation of cooling capacity
    By npaisnel in forum Domestic
    Replies: 13
    Last Post: 08-02-2002, 11:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •