    Frost Line method



    Evening all,

    Not to sure if this is in the right section but hey will try anyway.
    I hear a lot about Frost Line method of charging small refrigeration systems, can someone please explain to me what the hell this is and how it is done, because I have never ever come across this method?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Frost Line method

    With reference to your other questions I would stay well clear of this sort of thing.

    Concentrate on doing it right before trying the other ways.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2008
    Location
    Auckland
    Age
    55
    Posts
    264
    Rep Power
    21

    Re: Frost Line method

    Me thinks exam questions are being answered for this young fella.......

  4. #4
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    894
    Rep Power
    19

    Re: Frost Line method

    Hi there,

    In a small system with cap tube the amount of refrigerant is critical because cap tube can not do superheat control (like TEV) and therefore, liquid flood back is highly possible if overcharged.
    So, if the service tech does not know how to charge the system or if he does not use refrigerant scale then he assumes that when refrigerant flood back occurs then it is overcharged. Now how can he know that there is a flood back : by frosted suction line!!! When he sees the frost at the end of the cycle, he reduces the refrigerant charge so that the frost line goes back to wards the evaporator.
    This is common on the domestic refrigeration service techs.
    This is not a correct way. If want to charge a system then I suggest you learn the proper way.
    Cheers
    Even Einstein Asked Questions

  5. #5
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,045
    Rep Power
    35

    Re: Frost Line method

    In a nutshell, charge system wait until suction line frosts back then let a bit of the charge out until the frost starts to disappear.

    As has been noted NOT the correct way but that's how some people do it.

    Tried it myself once then weighed out the charge to see what I ended up with.
    Unit charge 800g, weighed out charge 850g. Not bad for a beginner I thought.
    Health and safety first..........unless I'm in a hurry.

  6. #6
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,094
    Rep Power
    23

    Re: Frost Line method

    So if your charging a domestic like I had to once (my own) my boss was a very experienced at it. Charge until you see the frost line when down to temp. Then remove/recover a little until the frost line disappears about two inches into the insulation. Do it a little at a time and observe over a few cycles.

  7. #7
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,847
    Rep Power
    21

    Re: Frost Line method

    The other way is to stop the evap fan from working .

    Charge the system till flood back is evident and then start the evap fan. When the fan is working the frost line will disapear.

    One reason why this method is not used is to do with ambient temps.

    If you charge the system up by using the frost back method in the winter it will be under charged in the summer. If you use the method in the summer it could be over charged in the winter..


    taz

    .

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 02:24 AM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. high liquid line pressure?
    By TECH TIM in forum Commercial
    Replies: 5
    Last Post: 09-05-2009, 05:36 PM
  4. Frost on suction line near compressor
    By ctct in forum Commercial
    Replies: 11
    Last Post: 04-02-2007, 12:44 AM
  5. Frost on the suction line
    By lana in forum Trouble Shooting
    Replies: 19
    Last Post: 22-01-2006, 07:04 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •