    Danfoss Controller EKC 202



    Hi Ya Folks,

    I am working on a boat as engineer. I have been having alarm go off on my Danfoss EKC 202 Controller.

    I mute the alarm via our ships alarm and monitoring system, I go to the control room and check the EKC Controller and the LEDS are flashing. I look at the temp and the controlller shows the temp are jumping from 0deg C to 12deg C and fluctuating up and down everywhere inbetween and I can here the Solenoid Valve opening and closing as the temps jump above and below the set point of 5.5deg C. I go to the fridge and the temp seems normal.

    To me it seems like it is a faulty temp probe, however I find out that recently another engineer has changed out the Temp Probe. However I also have a 30 minute time delay for temp alarm conditions. So could this be controller fault?

    What could be causing the alarm to go off?? We just have basic system for this fridge to keep it cool at around setpoint of 5deg C and alarm.

    I have now disconnected the wire for the alarm as it was going off at random time and annoying all fellow crew members.

    What you professionals think??? Could it be faulty controller? I have a spare, would it be worth the time and effort to change it out and see how things go?

    Any advice or input would be greatly appreciated from the Pro's who deal with these matters on a day to day basis.



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Danfoss Controller EKC 202

    Quote Originally Posted by Globe76 View Post
    Hi Ya Folks,

    I am working on a boat as engineer. I have been having alarm go off on my Danfoss EKC 202 Controller.

    I mute the alarm via our ships alarm and monitoring system, I go to the control room and check the EKC Controller and the LEDS are flashing. I look at the temp and the controlller shows the temp are jumping from 0deg C to 12deg C and fluctuating up and down everywhere inbetween and I can here the Solenoid Valve opening and closing as the temps jump above and below the set point of 5.5deg C. I go to the fridge and the temp seems normal.

    To me it seems like it is a faulty temp probe, however I find out that recently another engineer has changed out the Temp Probe. However I also have a 30 minute time delay for temp alarm conditions. So could this be controller fault?

    What could be causing the alarm to go off?? We just have basic system for this fridge to keep it cool at around setpoint of 5deg C and alarm.

    I have now disconnected the wire for the alarm as it was going off at random time and annoying all fellow crew members.

    What you professionals think??? Could it be faulty controller? I have a spare, would it be worth the time and effort to change it out and see how things go?

    Any advice or input would be greatly appreciated from the Pro's who deal with these matters on a day to day basis.
    check the power supply to the controller,if that is ok,change the controller.

Similar Threads

  1. Brochure for danfoss ekc 331 controller
    By abet_meneses in forum Supermarket Refrigeration
    Replies: 2
    Last Post: 18-10-2009, 12:35 AM
  2. Danfoss fan speed controller
    By jonb in forum Refrigeration Books
    Replies: 5
    Last Post: 11-05-2009, 11:56 PM
  3. Upgrading Danfoss AK2 controller
    By interop in forum Supermarket Refrigeration
    Replies: 2
    Last Post: 16-10-2008, 02:06 PM
  4. Danfoss EKC201C controller parameters
    By abd.koj in forum Supermarket Refrigeration
    Replies: 3
    Last Post: 23-03-2008, 10:25 PM
  5. Danfoss controller
    By chemi-cool in forum Chit Chat & Service Stories
    Replies: 2
    Last Post: 14-06-2007, 11:27 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •