14-06-2010, 06:49 PM #1
Determining Superheat!
Good evening all, what would you say is the best way to calvulate super heat, here are the two options i thought you could use, i just wanted to know what people thought was the best and mos accurate procedure.
1. Measure suction pressure at TEV bulb location and convert that to temperature using PT chart. Measure actual temperature at bulb location and compare the two, difference is the superheat.
OR
2. Firmly attach 2 thermometer probes one at evap inlet and other as close as possible to tev bulb, the temp difference between the two is the superheat.
What do u think is the best procedure?
-
14-06-2010, 07:45 PM #2
Re: Determining Superheat!
No 2 does not measure superheat, it just measures pipe temperatures.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
14-06-2010, 07:57 PM #3
Re: Determining Superheat!
Thanks very much Brian, I thought the first is a much more accurate way of calculating superheat. Thanks again
-
15-06-2010, 02:47 AM #4
Re: Determining Superheat!
Hi aaronh
Sorry to correct you but neither 1 or 2 are best. I am pedantic about accurate measurement. To calculate correctly you will need to first measure the temp of the refrigerant directly using a superheat calculation kit (yellow jacket ritchie) at the bulb location at the end of the cycle (and monitor during the cycle). Also check manufacturers compressor manual which sometimes indicates allowable SH at compressor. You can search this forum for further details.
-
15-06-2010, 08:27 AM #5
Re: Determining Superheat!
-
15-06-2010, 09:50 AM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Determining Superheat!
Tesla is also using manometers but he doesn't measure pipe temperature. Instead, he measure direct gas temperature by inserting tip of termometer inside copper pipe to direct stream of refrigerant gas. That eliminate one portion of transmission diference from gas to copper pipe and than to thermometer.
More precise and faster response.
http://www.yellowjacket.com/HVACRPro...l=7&c=76&p=136Last edited by nike123; 15-06-2010 at 10:09 AM.
-
06-07-2010, 10:24 AM #7
Re: Determining Superheat!
hi aaronh:For example if we have two comp in one circuite and we have unloader how we can detemine super heat?
-
06-07-2010, 11:41 AM #8
Re: Determining Superheat!
None of you consider the superheat picked up by the suction pipe.
The evaporator SH is the superheat measured on the evaporator outlet. The SSH is the superheat measured on the suction of compressor. It may vary considerably, especially on refrigeration circuit.
Similar Threads
-
9 superheat & subcooling scenarios
By nike123 in forum FundamentalsReplies: 39Last Post: 19-07-2011, 03:16 AM -
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Carrier 23xl chiller-Low discharge superheat alarms
By Bradysmill in forum Trouble ShootingReplies: 7Last Post: 25-04-2010, 07:43 PM -
Subcooling at TEV vs Superheat at Compressor relation in Steady State
By GXMPLX in forum FundamentalsReplies: 12Last Post: 14-07-2008, 03:00 PM -
Superheat
By shogun7 in forum FundamentalsReplies: 24Last Post: 23-08-2004, 05:54 PM