    Dear all,

    Please help me with the following design:

    I needed to design a room with the room size 10 ft x 20 ft, with ceiling height standard at 10 ft (approximately 3 meters)

    I wanted to maintain the room temperature at 16C constant.

    How and what information I needed to do the calculation for the above condition?



  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Design Problems

    put one air condition unit .it solve your request .

  3. #3
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Design Problems

    YOu shall need to find out the product load if any.

    For that you need product loading rate, its incoming temp & cooling period.

    That shall take you to the total heat heat load needed & select the unit for matching capacity.

  4. #4
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: Design Problems

    Quote Originally Posted by weeliang82 View Post
    Dear all,

    Please help me with the following design:

    I needed to design a room with the room size 10 ft x 20 ft, with ceiling height standard at 10 ft (approximately 3 meters)

    I wanted to maintain the room temperature at 16C constant.

    How and what information I needed to do the calculation for the above condition?
    Hope this helps
    http://www.daikinindia.com/onlinesolutions_plaza.asp

  5. #5
    Join Date
    Nov 2009
    Location
    Malaysia
    Age
    41
    Posts
    31
    Rep Power
    0

    Re: Design Problems

    Dear all,

    I appreciate all your reply here but can you guys try to give me an example on what I needed to find in order for me to solve the problem?

    For example, product loading rate, incoming temp, cooling period..

    I needed to maintain the temp at 16C and the design conditions is probably:

    Indoor DB = 27 C
    Indoor WB = 19 C
    Outdoor DB = 35 C

    Please help... Thanks

  6. #6
    Join Date
    Mar 2008
    Location
    England
    Posts
    232
    Rep Power
    20

    Re: Design Problems

    You will ave to provide a lot more information if you are get help from the members.
    What is the room to be used for?
    Is this a process facility is so what equipment is in the room?
    Are there windows, if so which way do they face?
    Is a ground floor if not how many floors are below it?
    What is the roof design?
    How many people are in the room.?
    Do you have a RH you need to maintain in addition to your 16C DB?
    The more detail you can provide I am sure there will be lots of help from this forum.

  7. #7
    Join Date
    Feb 2008
    Location
    IRELAND
    Posts
    70
    Rep Power
    17

    Re: Design Problems

    Is standard a/c meant to hold rooms below 18? MHI units dont go any lower than this. Obviously air off temps are lower but is it sustainable?

Similar Threads

  1. Problems in r22 chiller design
    By umeshpradhan in forum Technical Discussions
    Replies: 9
    Last Post: 06-07-2010, 10:39 AM
  2. Replies: 3
    Last Post: 28-01-2008, 08:29 PM
  3. Efficient Water-Source Condenser Design?
    By Enginerd in forum Fundamentals
    Replies: 4
    Last Post: 28-05-2007, 05:11 AM
  4. Replies: 31
    Last Post: 28-11-2006, 10:32 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •