    Talking excessive superheat orifice help



    Hi Everyone

    Where superheat is excessive (despite adjusting TEV)
    can anyone tell me if it's worth going up an orifice size, say from 0-1?

    If not, why not?

    This particular job was designed by someone else and it's a bit of a one off.

    Thanks.



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: excessive superheat orifice help

    If on comissioning a system it apears the txv is underfeeding the evap, i don't see anything wrong with trying the next size up orifice.

    Does the system have a distributor after the txv? one system i got called in to look at for a friend had one that was set up horizontally with one capilliary above the other, in effect only the bottom cap saw any liquid and only half the evap did any work, we truned the distributor through 90' so both caps were side by side and the system worked as intended.

    Jon

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: excessive superheat orifice help

    May require an externally equalized TXV, to compensate coil pressure loses.

  4. #4
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: excessive superheat orifice help

    are you sure it is the TEV that is causing the malfunction? is the evaporator correctly calculated? are the lines the correct diam., and so on and on....and on....an...

  5. #5
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: excessive superheat orifice help

    Thanks everyone

    I'm not sure now if the superheat is excessive, it's only a small fridge with quite a long run (10m) and i'm having to take my sat. pressure at the outdoor unit. Also I only took a couple of readings on the suction pipe and maybe didn't leave enough time for the valve to react blah blah blah

    but thanks anyway

Similar Threads

  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Replies: 39
    Last Post: 19-07-2011, 03:16 AM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 02:24 AM
  3. Replies: 12
    Last Post: 14-07-2008, 03:00 PM
  4. Excessive Superheat
    By AEGIS Cool in forum Technical Discussions
    Replies: 13
    Last Post: 26-11-2006, 09:06 PM
  5. superheat with the wrong orifice
    By superheat in forum Air Conditioning
    Replies: 9
    Last Post: 25-10-2002, 08:54 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •