    Mitsi Electric PUHZ RP10 KVA Compressor will not run



    This unit has been insalled about a week and was running great, but got a call to go and check the unit this eve (outdoor model PUHZ RP10KVA) about the unit not cooling.

    Turned the unit on and the fans run outside for about 2 secs then off and repeats this about 5 times.

    The outdoor unit is flashing fault code 3 green and 4 red .

    I took the 3 wires off compressor and checked windings, 2 are 1.0 ohms and the other is 0.9.

    When power is turned on with these wires disconnected thetre is 23.4v between 2 phases DC and the same fault code appears with the wires disconnected.

    I have checked compressor wires where they go onto board and all seems fine.

    Has anyone had this problem ?

    Regards

    Chris



  2. #2
    Join Date
    Jan 2005
    Location
    N.Ireland
    Age
    48
    Posts
    177
    Rep Power
    20

    Re: Mitsi Electric PUHZ RP10 KVA Compressor will not run

    Faulty power board

  3. #3
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Mitsi Electric PUHZ RP10 KVA Compressor will not run

    hi chris

    i recently ran up a mitsi system and had a problem where the compressor was making a noise and failing to start
    had error lights cant remember what these were now.

    turned out to be a faulty power board.

    cheers lee

  4. #4
    Join Date
    Jan 2005
    Location
    N.Ireland
    Age
    48
    Posts
    177
    Rep Power
    20

    Re: Mitsi Electric PUHZ RP10 KVA Compressor will not run

    Hi lee

    The compressor on this unit was doing nothing at all, the fans were the only thing that would run.
    only the red wire was live to comp the other 2 nothing.

    Its the first time this has happend to me normally mitsi are very reliable.

    Regards

    Chris

  5. #5
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Mitsi Electric PUHZ RP10 KVA Compressor will not run

    Quote Originally Posted by Chris2005 View Post
    Hi lee

    The compressor on this unit was doing nothing at all, the fans were the only thing that would run.
    only the red wire was live to comp the other 2 nothing.

    Its the first time this has happend to me normally mitsi are very reliable.

    Regards

    Chris
    i remember that all wires were live on mine, they were fluctuating i think just over a 100 volts i was told by mitsi that its the power board. someone fitted the power board and its all working now.

    cheers lee

  6. #6
    Join Date
    Jan 2005
    Location
    N.Ireland
    Age
    48
    Posts
    177
    Rep Power
    20

    Re: Mitsi Electric PUHZ RP10 KVA Compressor will not run

    My new part will be here in the morning thankfully

    Which should save a little ear bashing from the customer

  7. #7
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Mitsi Electric PUHZ RP10 KVA Compressor will not run

    good luck let us know that it was defo the power board

    cheers lee

  8. #8
    Join Date
    Jan 2005
    Location
    N.Ireland
    Age
    48
    Posts
    177
    Rep Power
    20

    Re: Mitsi Electric PUHZ RP10 KVA Compressor will not run

    Hi lee

    I got the new board this afternnon and replaced it this evening.
    I am pleased to say everything is working fine now ,

    What part of manchester are you from?

  9. #9
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Mitsi Electric PUHZ RP10 KVA Compressor will not run

    hi chris glad to hear it. i am from urmston what about yourself?

    just noticed northern ireland :-)

  10. #10
    Join Date
    Jan 2005
    Location
    N.Ireland
    Age
    48
    Posts
    177
    Rep Power
    20

    Re: Mitsi Electric PUHZ RP10 KVA Compressor will not run

    Hi lee

    My grandad used to live in flixton beside woodsend circle , I have a lot of family around that area as I was born there myself .
    Hows the fridge trade over there at the min?

    Regards

    Chris

  11. #11
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Mitsi Electric PUHZ RP10 KVA Compressor will not run

    hi chris yeah know it well lived here all my life.

    its picking up at the company i work for, got quite a lot of work on so its very busy at the moment mate

Similar Threads

  1. Replies: 4
    Last Post: 12-06-2010, 09:45 PM
  2. Mitsi electric fault codes?
    By weidit in forum Air Conditioning
    Replies: 15
    Last Post: 22-12-2009, 10:54 PM
  3. Mitsi Electric RP6AA Pump Fault
    By gwilliamson in forum Air Conditioning
    Replies: 8
    Last Post: 15-08-2008, 05:59 PM
  4. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 05:11 PM
  5. Mitsi electric large.
    By Simon Butler in forum Air Conditioning
    Replies: 7
    Last Post: 29-10-2007, 10:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •