    how can I raise the pressure for chilled water project



    Hi all,
    I have a problem on my hand:
    I have chilled water project with primary and secondary pumps. The primary loop consist of Three small pumps to ensure that the three chillers we have never starve for water. Each pump is about 15 HP. Now the secondary pumps consist of two on duty and one stand by pump. Each pump is about 50 HP and can push up to 1300GPM. The problem I have is that the water coming from the chillers to the secondary pump is arriving at 65 psi but the pressure at the pump outlet is dropping to 25-30 PSI. This means that my project is getting chilled water at 25-30 PSI which is too low because my highest point of demand is at 35 meters and I need about 60PSI to get it up there. The reason the pressure is high at the inlet of the secondary pumps "I would presume" is because the primary pumps are pushing the water at this PSI. How can I get the pressure to the net work to go up?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: how can I raise the pressure for chilled water project

    Can your secondary pumps produce the required pressure/flow without the primary pumps running?

    If not then you need to investigate that problem first.

    Does the primary loop feed a low-loss header for the secondary side to take the chilled water from?

    Are all of the pumps running with the correct rotation?

    Is this the chilled water system that you were referring to when asking about PVC pipework over two and a half years ago? Because we never did hear back from you concerning the answers given.
    Last edited by Brian_UK; 12-06-2010 at 10:58 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: how can I raise the pressure for chilled water project

    Quote Originally Posted by Brian_UK View Post
    Can your secondary pumps produce the required pressure/flow without the primary pumps running?

    If not then you need to investigate that problem first.

    Does the primary loop feed a low-loss header for the secondary side to take the chilled water from?

    Are all of the pumps running with the correct rotation?

    Is this the chilled water system that you were referring to when asking about PVC pipework over two and a half years ago? Because we never did hear back from you concerning the answers given.
    are water strainers clean???
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  4. #4
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: how can I raise the pressure for chilled water project

    It seems you have insufficient secondary pumps TDH, which is a design issue. You can check the Head of the secondary pumps by looking at its performance curve/graph to see if it would match your system requirements.
    Also, what is the chilled water return suction pressure on your primary pumps?,you can try to run 1 more secondary pump in parallel with the 2 pumps to increase both the flowrate and pressure. Check also the volume of water inside your pipe loops, lack of water also makes the pressure down.
    Pls. give us your feedback..
    <"No one is so smart, they just stay with problems longer and use their imagination">

  5. #5
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: how can I raise the pressure for chilled water project

    Strange - as you wrote you have 65 psi at the inlet and 25 psi at the outlet of the secondary pumps. Is there a blockage, cavitation and are the pumps running in the correct direction? Are the inlet and outlet pipes sized correctly?

Similar Threads

  1. Hoshizaki Ice Maker
    By Abe in forum Legal-Business-Marketing
    Replies: 19
    Last Post: 01-05-2010, 03:27 AM
  2. About liuid line pressure drop.
    By wilsoncheung in forum Technical Speculations
    Replies: 15
    Last Post: 16-03-2009, 11:34 AM
  3. Drinking Fountain / Water Cooler
    By shinglai in forum Fundamentals
    Replies: 3
    Last Post: 10-03-2009, 06:38 PM
  4. household water line pressure
    By andrei in forum Fundamentals
    Replies: 3
    Last Post: 02-05-2002, 04:44 AM
  5. Psychrometrics
    By Prof Sporlan in forum Fundamentals
    Replies: 12
    Last Post: 01-12-2001, 06:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •