    On remote unit, will t-stat directly control the compressor on and off?



    for commercial refrigeration



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: On remote unit, will t-stat directly control the compressor on and off?

    It will control it but probably via a contactor or other start device.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: On remote unit, will t-stat directly control the compressor on and off?

    Quote Originally Posted by Brian_UK View Post
    It will control it but probably via a contactor or other start device.
    Could you give an example? Thanks.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: On remote unit, will t-stat directly control the compressor on and off?

    Quote Originally Posted by david2008 View Post
    Could you give an example? Thanks.
    You jest surely ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: On remote unit, will t-stat directly control the compressor on and off?

    Quote Originally Posted by Brian_UK View Post
    You jest surely ?
    I am rookie.

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: On remote unit, will t-stat directly control the compressor on and off?

    Quote Originally Posted by david2008 View Post
    Could you give an example? Thanks.

    Have a look on youtube for vids on refrigeration contactors etc, i have tried to put a link in but can't get them to work for some reason


    Jon
    Last edited by monkey spanners; 13-06-2010 at 11:03 AM.

  7. #7
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: On remote unit, will t-stat directly control the compressor on and off?

    Thanks Jon. If the remote condenser is located 300feet away, does it need 300feet long wiring?

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: On remote unit, will t-stat directly control the compressor on and off?

    Hi David,

    It depends on the system, you could wire the condenser fan/s back to the compressor control panel, or you could run it off a pressure switch or fan speed control so it will start up once the system pressure rises.

    As the tech installing the sytem the choice is yours, many factors will influence your decission as to the best method for the system in question.

    300ft is a long distance for a remote condenser, much thought would need to be put into pipe sizing and routing.

  9. #9
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: On remote unit, will t-stat directly control the compressor on and off?

    It makes sense. Thank you Jon!

    Quote Originally Posted by monkey spanners View Post
    Hi David,

    It depends on the system, you could wire the condenser fan/s back to the compressor control panel, or you could run it off a pressure switch or fan speed control so it will start up once the system pressure rises.

    As the tech installing the sytem the choice is yours, many factors will influence your decission as to the best method for the system in question.

    300ft is a long distance for a remote condenser, much thought would need to be put into pipe sizing and routing.

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: On remote unit, will t-stat directly control the compressor on and off?

    Quote Originally Posted by david2008 View Post
    I am rookie.
    OK David, fair comment.

    There are some wiring schematics on this Emmerson link which may prove useful.

    http://www.emersonclimate.eu/literat..._C070901_0.pdf

    Regarding your later question about 300ft....

    If there are fair distances between indoor and outdoor you may often find that the power circuits/supply are adjacent to the outdoor unit and a low(er) voltage signal wire will be used from the indoor unit. So wiring diagrams, although compact, can cover a large area.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: On remote unit, will t-stat directly control the compressor on and off?

    Thank you Brian. I will read the pdf file you provided. 300feet is just an “if” number. It looks like too far…….. what is a average distance for remote system? Less than 100 feet?

    Quote Originally Posted by Brian_UK View Post
    OK David, fair comment.

    There are some wiring schematics on this Emmerson link which may prove useful.

    http://www.emersonclimate.eu/literat..._C070901_0.pdf

    Regarding your later question about 300ft....

    If there are fair distances between indoor and outdoor you may often find that the power circuits/supply are adjacent to the outdoor unit and a low(er) voltage signal wire will be used from the indoor unit. So wiring diagrams, although compact, can cover a large area.

  12. #12
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: On remote unit, will t-stat directly control the compressor on and off?

    Remote can be just outside the building or across a car park.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  13. #13
    Join Date
    Feb 2009
    Location
    USA
    Age
    54
    Posts
    143
    Rep Power
    16

    Re: On remote unit, will t-stat directly control the compressor on and off?

    Hey, the t-stat controls the selenoid (pump down system in your case) located next to the evaporator, low pressure contro; shuts dowm compressor. No, you don't need a 300' wire, that extra wire will kill your compressor sooner than you might think.

  14. #14
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: On remote unit, will t-stat directly control the compressor on and off?

    Thanks for response. I understand your post that solenoid and low pressure control can work together to on and off the compressor. Just now, when I read the online information, there are also high pressure control and dual pressure control. How did the high and dual pressure control work to make compressor on and off? Do they still use solenoid? Thanks. David.

    Quote Originally Posted by Royal241 View Post
    Hey, the t-stat controls the selenoid (pump down system in your case) located next to the evaporator, low pressure contro; shuts dowm compressor. No, you don't need a 300' wire, that extra wire will kill your compressor sooner than you might think.

  15. #15
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: On remote unit, will t-stat directly control the compressor on and off?

    High pressure switch turns the compressor off if the condensing pressure get to high for some reason, e.g. dirty condenser, failed fan motor, very high ambient temperature. A HP switch can also be used to cycle condenser fans on and off on multi fan condensers to keep a more constant condensing pressure.

    A dual control is just a Low pressure and high pressure switch combined into one housing. (Be carefull when swaping diffent makes as a replacement because some are LP/HP and some go HP/LP so if you put the capiliaries on the same side you took them off they would then go to the wrong switch!!!)

    Jon

  16. #16
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: On remote unit, will t-stat directly control the compressor on and off?

    Thank you Jon!


    Quote Originally Posted by monkey spanners View Post
    High pressure switch turns the compressor off if the condensing pressure get to high for some reason, e.g. dirty condenser, failed fan motor, very high ambient temperature. A HP switch can also be used to cycle condenser fans on and off on multi fan condensers to keep a more constant condensing pressure.

    A dual control is just a Low pressure and high pressure switch combined into one housing. (Be carefull when swaping diffent makes as a replacement because some are LP/HP and some go HP/LP so if you put the capiliaries on the same side you took them off they would then go to the wrong switch!!!)

    Jon