    Hitachi capacity problem



    Got sent to site today to look at a Hitatchi utopia DC Inverter ras-8grnm.

    Found system with no cooling and compressor frequency at 30hz due to discharge temp reading of 101DegC, indications of short of gas.

    Recovered refrigerant, found the leak and repaired, however when i turned system back on i got a fault code of "31" on the outdoor board.

    31 is Incorrect Capacity Setting or Combined Capacity between Indoor Units and
    Outdoor Unit.

    I checked DSW3 was set correctly although i hadnt been near the boards so could no way have accidentally switched a dip switch.

    I checked all the dip switches were set as they should be and reset power but still i'm getting the incorrect capacity setting.

    The unit has been running fine for 18 months.

    Has anyone ever come across this before?
    Last edited by marc5180; 12-06-2010 at 08:42 PM.


    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Join Date
    Jan 2009
    Location
    scotland
    Posts
    9
    Rep Power
    0

    Re: Hitachi capacity problem

    a 31 code can also mean that power has been lost to a indoor unit .turned off power for indoor unit while other indoor units are running. this results in a differant setting of the total indoor unit capacity in the same refrigerant cycle. hope this helps

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Hitachi capacity problem

    Hi Richard, thanks for the reply.

    The problem was a blown fuse on the indoor board but i had to hire scaffold to get up to the unit as it was high level.

    All sorted now
    The difference between genius and stupidity is that genius has its limits.

    Marc

Similar Threads

  1. York DXS45 capacity slide problem
    By The Screwdoctor in forum Industrial Compressors
    Replies: 8
    Last Post: 25-05-2010, 04:40 AM
  2. DX capacity lower than condensing unit
    By M.Saleh in forum Trouble Shooting
    Replies: 5
    Last Post: 17-01-2010, 09:29 PM
  3. Well Done / Thanks Hitachi UK
    By Latte in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 24-11-2008, 07:52 PM
  4. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM
  5. Hitachi AC Invertor Problem
    By martin ice in forum Air Conditioning
    Replies: 4
    Last Post: 20-02-2008, 10:28 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •