    Refrigerant loss from Hansen auto purger



    Hello all,

    I am faced with a current dilemma that you can help me answer. I work for a plant that has ~50k lbs nh3 charge. Four operating pressure systems, 7"hg, 24psig, 30psig, and condensing of 124-135 (design).

    We are currently purging from the condensing pressure, and the suction for our ap24 is at 24psig. The two highest of our four condensor receive 6 purge points each, at 15 min intervals. The two lowest receive 6 purge points ea at 5 min intervals. There is half inch purge line coming from each of the purge points into a common half in header. The total length of each purge line is about 250ft.

    Problem: I think I am losing a lot of refrigerant through the purger. Upon observation the bubbler appears to function fine, but short of watching it all day I could not confirm this. It has been suggested that the check valve is faulty, which I will check today. Hansen said that the unit is designed to use a 30# check valve. Sometimes the discharge end of the purger can get up to 32-37 psig for about 20min (from the normal 24psig).

    Thanks ahead of time.



  2. #2
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Refrigerant loss from Hansen auto purger

    The purger would work much better if the suction was piped to your lower temperature suction (7"hg).

  3. #3
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Refrigerant loss from Hansen auto purger

    Quote Originally Posted by simplygold View Post
    Hello all,

    I am faced with a current dilemma that you can help me answer. I work for a plant that has ~50k lbs nh3 charge. Four operating pressure systems, 7"hg, 24psig, 30psig, and condensing of 124-135 (design).

    We are currently purging from the condensing pressure, and the suction for our ap24 is at 24psig. The two highest of our four condensor receive 6 purge points each, at 15 min intervals. The two lowest receive 6 purge points ea at 5 min intervals. There is half inch purge line coming from each of the purge points into a common half in header. The total length of each purge line is about 250ft.

    Problem: I think I am losing a lot of refrigerant through the purger. Upon observation the bubbler appears to function fine, but short of watching it all day I could not confirm this. It has been suggested that the check valve is faulty, which I will check today. Hansen said that the unit is designed to use a 30# check valve. Sometimes the discharge end of the purger can get up to 32-37 psig for about 20min (from the normal 24psig).

    Thanks ahead of time.
    Why do you think that you lose ammonia through the purger? Charlie N is right that purger will waste less ammonia at lower suction pressure.

  4. #4
    Join Date
    Jul 2005
    Location
    USA
    Age
    61
    Posts
    68
    Rep Power
    19

    Re: Refrigerant loss from Hansen auto purger

    There should be three check valves, 1 PSID, 30 PSID and 200/225 PSID.
    The check valves are parts that Hansen included in the overhaul kit. So they a wear items. And I have sold a few over the years.
    The 1 PSID valve is on the line to the bubbler. Check to make sure it is a 1 PSID and not a 30 PSID. That would explain the high pressure reading. Or it could just be a wore out check valve.

  5. #5
    Join Date
    Aug 2010
    Location
    UK
    Posts
    110
    Rep Power
    14

    Re: Refrigerant loss from Hansen auto purger

    If it is an Auto purger then best to throw it away and fit a NEAP! I have recently done this and my purge problems have almost dissappeared.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. which refrigerant ???????
    By bob007 in forum Trouble Shooting
    Replies: 28
    Last Post: 31-05-2010, 12:54 PM
  3. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •