    Unhappy Compressor safety valve opens



    Sir,
    I am installing 7 nos 5TR condensing unit with reciprocation compressor, emerson make, in our one site in India. Unfortunately, we are observing one problem which I never faced. Kindly advise me.
    During charging of refrigerant when suction pressure reaches 50-55 psi & discharge pressure reaches 260-70 psi the safety valve opens & compressor trips.



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Compressor safety valve opens

    i DONT KNOW WHAT REFRIGERANT YOUR ON, but it looks like a faulty compressor?

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Compressor safety valve opens

    What Sedgy said, also where are you measuring the pressure and how quick are you charging?

    I'm not familiar with these safety valves, do they work on temperature or pressure differential?

    Jon

  4. #4
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: Compressor safety valve opens

    -are the safety valves rated at 250 psi or higher?
    -Where is the HP manometer connected?

    I had a problem on a twin howden unit (2 compressors on one oil sep) where we measured the HP on the common HP line, both compressors had danfoss NRV/CHV valves fitted


    The SFV valve was fitted between the compressor and NRV.

    When the compressor reached 70% capacity the gas detector in the safety line tripped.

    I fitted a manometer on the line next to the sfv, and while we had a normal 10 bar in the common line it was 22 bar before the NRV.

    being in south america and parts were hard to come by, I took the lid of the NRV, and took off 10 mm in the lathe so that the valve could open further and problem solved.
    -Cheers-

    Tycho

  5. #5
    PRADYUTGHOSH's Avatar
    PRADYUTGHOSH Guest

    Re: Compressor safety valve opens

    Sir,
    It is Hermatically sealed reciprocating compressor. Refrigerant is *****-22. The safety valve setting is factory setting of Emerson.
    Is there any relation with condenser size?

  6. #6
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: Compressor safety valve opens

    Quote Originally Posted by PRADYUTGHOSH View Post
    Sir,
    It is Hermatically sealed reciprocating compressor. Refrigerant is *****-22. The safety valve setting is factory setting of Emerson.
    Is there any relation with condenser size?
    and what is the factory setting? is the valve set to open at 250 psi?

    seems kinda low for the HP side
    -Cheers-

    Tycho

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Compressor safety valve opens

    Quote Originally Posted by Tycho View Post
    and what is the factory setting? is the valve set to open at 250 psi?

    seems kinda low for the HP side

    I think they work on differential pressure too so it would be operating at around 200/210psi which seem way too low to me!

    What is the run currnet when it trips? and what is the max run current for the compressor? would give an idea of how hard the compressor is working when the valve lets go. Maybe the compressor is seeing a higher pressure than your gauges due to a restiction in the pipework, where are you measuring the high side pressure?

    I think on these hermetic compressors the valve is fitted on the muffler inside the compressor body and not on the head, i know some scroll comps valves work on temperature so thats why i wondered about the discharge superheat, if the system is low on charge it would have a high superheat.

    Jon

  8. #8
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Compressor safety valve opens

    PRADY,

    I believe you're referring to the IPR (internal pressure relief valve) which is designed to open when the discharge to suction differential exceeds 450 to 550 psid.

    Check for restrictions in the discharge line or an overcharged system.

    Here's a link that will help you out.

    http://www.hvacrinfo.com/ae_index.htm

    section 4-1329.
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

Similar Threads

  1. Howden slide valve problems
    By CanadianIce in forum Industrial Compressors
    Replies: 9
    Last Post: 29-06-2010, 04:38 PM
  2. LEV does not open
    By Yuri B. in forum Air Conditioning
    Replies: 7
    Last Post: 19-07-2009, 02:37 PM
  3. R22 Flooded System - Trawler
    By chiefbecker in forum System Optimization
    Replies: 18
    Last Post: 07-02-2008, 11:11 PM
  4. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  5. Replies: 5
    Last Post: 16-10-2002, 12:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •