    ammonia pump problem



    can anyone help me about ammonia recirculation pump?

    we are using ammonia over feed system in our cold storage, when we run the compressor the pump get down! without compressor the ammonia runs at 7 kgs without any problem but when we run the compressor the pump get down.

    please help me out!



  2. #2
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,035
    Blog Entries
    4
    Rep Power
    31

    Re: ammonia pump problem

    Quote Originally Posted by Sukhvinder View Post
    can anyone help me about ammonia recirculation pump?

    we are using ammonia over feed system in our cold storage, when we run the compressor the pump get down! without compressor the ammonia runs at 7 kgs without any problem but when we run the compressor the pump get down.

    please help me out!
    What kind of pump are you using, and how is it piped?


    it is possible that when you start the compressor, you get boiling in the ammonia and the pump cavitate because it's not pumping pure liquid.
    -Cheers-

    Tycho

  3. #3
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: ammonia pump problem

    I agree with Tycho. Start the compressor at low capacity and increase the capacity slower. The problem maybe occurs after the liquid be very hot (high saturated temperature) and with the high decrease rate of the suction there is much formation of vapour on the middle of the liquid.
    To make progress is never good enough, I want to do better and better and better

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: ammonia pump problem

    One item to consider: start the compressors first to reduce the suction pressure and liquid temperature with the pump off. This will cool down the pump. Then let the compressor unload to maintain the lower temperature. after the pump begins to cool for about 30 minutes you can try to start the pump then. Do not let the compressor capacity increase too much. if it does, the pump may cavitate again.
    If all else fails, ask for help.


  5. #5
    Join Date
    Dec 2005
    Location
    Norfolk, England
    Age
    66
    Posts
    132
    Rep Power
    19

    Re: ammonia pump problem

    Hi, just for info on our new LT surge drum we had fitted last year with Hermetic liquid Ammonia pumps. One of them will start at -0.4 Bar and pump well but the other one will only start around zero Bar. They came from the same producting line and the serial numbers follow each other and are rated at the same duty. The makers can not say why we have this problem with them.

  6. #6
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: ammonia pump problem

    All of advice for running compressor is right , you have to run first compressor and after you system be come to your design temperature then start your pump also on - off of compressor should not have a too much difference.
    But to install NH3 pump you have to be careful.

    Size of inlet and out let and slope of inlet pipe is very important and also to chose right type pump with right head.
    Last edited by mbc; 17-06-2010 at 07:13 PM.

  7. #7
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: ammonia pump problem

    I agree Iceman, start the compressor first manually at reduced load and wait for the surge drum pressure to stabilize before starting your ammonia pumps. But remember not to put too much load on your pumps during its start-up. Load your evaporators one by one until your system stabilizes.
    <"No one is so smart, they just stay with problems longer and use their imagination">

  8. #8
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,035
    Blog Entries
    4
    Rep Power
    31

    Re: ammonia pump problem

    if the pumps are piped correctly you shouldnt need to run the system by hand.


    on all our pumps we have a t-connector on the pump suction the same size as the suction pipe, on top we put a reducer to 2" and a pipe up to the liquid separator again to allow most of the flash gas to escape.

    I have never had a pump with delivery pressure problems because the compressor loads to fast, sure I've seen it oscillate from 2.5- 3 bar, but never loosing the pressure completely.

    but we are missing some info, cause he says he has 7 bar pump pressure with only the pumps, but not by how much it drops.

    and in any regard, 7 bar is pretty high for a liquid pump
    -Cheers-

    Tycho

  9. #9
    Join Date
    Dec 2006
    Location
    Iran
    Age
    43
    Posts
    55
    Rep Power
    18

    Re: ammonia pump problem

    Dear friends,
    I think that it migt be cause of the lack of ammonia in system. by the way if this is not true tell me.
    thanks

  10. #10
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: ammonia pump problem

    For using refrigerant pumps it is always best practice to have a low pressure receiver from where the suction gas is taken to the compressor suction and pump suction is connected to the low pressure receiver.The liquid from condenser/receiver is fed to the low pressure receiver.

    If the above is followed pump may cavitate only when the total refrigerant charge is less due to some leak.

  11. #11
    Join Date
    Apr 2008
    Location
    canada
    Age
    75
    Posts
    94
    Rep Power
    17

    Re: ammonia pump problem

    Tycho,
    If I understood you correctly, that you place a tee near the suction port of the pump going directly to the pump. The “up” portion of the tee is reduced to 2” connected to the top part of the liquid separator. Is it correct? Would not be the same to pipe from the receiver down to the pump with a bigger dia. pipe to allow bubbles to escaped up to the receiver and then to reduce it the size of the suction port without the tee.

Similar Threads

  1. Temperature problem with liquid NH3
    By energeia in forum NH3
    Replies: 34
    Last Post: 05-08-2009, 08:16 AM
  2. problem with an hermetic pump
    By luissandoval in forum NH3
    Replies: 4
    Last Post: 14-01-2009, 07:07 AM
  3. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  4. Liquid Ammonia Pump problems
    By smpsmp45 in forum NH3
    Replies: 7
    Last Post: 01-02-2008, 11:51 AM
  5. ammonia refrigeration
    By deepakrbhat in forum Refrigerants
    Replies: 77
    Last Post: 23-04-2004, 12:07 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •