    can anyone help me about ammonia recirculation pump?

    we are using ammonia over feed system in our cold storage, when we run the compressor the pump get down! without compressor the ammonia runs at 7 kgs without any problem but when we run the compressor the pump get down.

    please help me out!




  2. #2
    mimo's Avatar
    mimo Guest

    Re: ammonia pump problem

    Sir,
    maybe you are using a small capacity NH3 pump. Better replace it with a bigger capacity..

  3. #3
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: ammonia pump problem

    What changed? Pump? Liquid Level? Count of Evaps? Thsi pump spinning but not making pressure or cutting off due to a control/electrical/lqiudi level issue? What is make and model of pump and how the liquid level in the vessel controlled and measured? Can you make some sketch of how the delivery from the vessel to the pump is piped? Details count....

    With compressor running: refrigerant in the vessel is being cooled by its own evaporation....Makes bubbles.
    Pump inlet flow can simply pick up the bubbles and you will have little pressure pulsations and some rattling at the pump impellor...so the velocity down the suction leg has to be low enough that the bubbles rise and don't get sucked down by the moving liquid....so your vessel and its liquid level and the piping between have to be large enough and high enough need to both prevent and deal with the bubbles....BUT:

    Refrigerant in pump and immediately upstream of pump can then do a number of different things: if there is a vapor pocket trapped within a non-operating pump, it will grow as the pressure reduces; and the pump may not be able to clear it. Really bad piping will introduce the "pocket" of the non-operating pump, to the suction of the operating pump. Same sort of thing can happen in the immediate upstream piping even under flow.... Large high point in that portion of pipe tends to accumulate vapor; and soomer or later pocket of vapor grows and gets pushed into pump housing. Big jerk, sometimes, but can also completely stop flow.

    Depending on nature of the pump: It can swirl the incoming flow which develops a vortex where the suction pipe enters the vessel (like flushing a toilet) and there will be a "tube" of vapor all the way to the pump inlet; add that to the "wrong" inlet piping geometry and you will collect vapor in a portion of suction pipe such that it can't rise back to the vessel; eventually it grows and seals the pump's suction cavity from the vessel liquid and the pump drinks the "void" and all flow stops....

    Conventional cavitation occurs when the liquid moves very fast with respect to the blades of the impellor; so fast that cavities of vapor are left on the backside of every impellor vane...the vapor travels toward the discharge of the pump and the higher local pressure causes the cavity to collapse: iitsounds like gravel is going through the pump, in most case. And its very rough on seals, bearings, impellor surfaces and so on.

    Mostly: this type can be cleared by stopping the pump; close the discharge down to a very small opening; start the pump; open discharge very slowly. If the pump discharge pressure does not twitch: it should start high and decrease as you permit the pump flow to increase. If you are asking for too much flow from the pump: the discharge pressure will start to surge and swing and twitch before the discharge valve is all the way open.

    Describe for us what's gone on to change any of these characteristics and maybe we can help...But maybe not, too.

  4. #4
    Join Date
    Dec 2008
    Location
    usa
    Age
    83
    Posts
    34
    Rep Power
    0

    Re: ammonia pump problem

    good analysis, Sterl...you could be an old fart like me..........maybe we know each other.

  5. #5
    Join Date
    Oct 2007
    Location
    w.mids
    Age
    49
    Posts
    110
    Rep Power
    17

    Re: ammonia pump problem

    Thanks for that little lesson.
    Put the screwdriver down and step away from the expansion valve !!!! OK Gary i won't touch it unless instructed.

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: ammonia pump problem

    Rapid pull down will create cavitation at the pump infeed. So slow down the compressor loading rates. Soft and easy slow and controlled.
    The pump should be at least 2 metres below the accumulator with anti cavitaion plate in place. Plus votex plate before pump inlet.

  7. #7
    Join Date
    Mar 2010
    Location
    INDIA
    Age
    57
    Posts
    7
    Rep Power
    0

    Re: ammonia pump problem

    I am in india .Pl call me 09335921043

Similar Threads

  1. Temperature problem with liquid NH3
    By energeia in forum NH3
    Replies: 34
    Last Post: 05-08-2009, 08:16 AM
  2. problem with an hermetic pump
    By luissandoval in forum NH3
    Replies: 4
    Last Post: 14-01-2009, 08:07 AM
  3. Ammonia liquid pump
    By jessica in forum NH3
    Replies: 19
    Last Post: 30-05-2008, 12:53 PM
  4. Liquid Ammonia Pump problems
    By smpsmp45 in forum NH3
    Replies: 7
    Last Post: 01-02-2008, 12:51 PM
  5. ammonia refrigeration
    By deepakrbhat in forum Refrigerants
    Replies: 77
    Last Post: 23-04-2004, 12:07 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •