Im just getting into the refrigeration field, I am getting exposed to supermarket refrigeration mainly. So that means I will be working on rack systems. I got a chance to look at a control panel and was simply amazed. One question that has been bugging me is what the function of an auxillary contactor is? Basically there were three breakers for each of the compressors, but there were four contactors, and i was told thats an auxillary contactor... I didnt get a chance to ask why it is used. All what was told to me dont have both of them engerized. Can anybody help me out?
-
11-06-2010, 06:01 AM #2
Re: Auxillary Contactor
Try a career change to something that you understand and are comfortable with.
-
11-06-2010, 11:46 PM #3
Re: Auxillary Contactor
Perhaps it is relating to the motor starter.
Depending on size the start method changes, try looking at start/delta or part wind starting systems.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
12-06-2010, 12:13 PM #4
Re: Auxillary Contactor
Hi Kevin welcome to the site. The term auxillary contactor normally used when the cotactor is used in the control circuit for performing a logical operation rather than used as normal power contactor.
-
13-06-2010, 09:17 AM #5
Re: Auxillary Contactor
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
13-06-2010, 10:11 AM #6
Re: Auxillary Contactor
Just a thought that i'm wondering, you say the comps have three breakers, so i assume they are three phase comps, then you say they have four contactors, this could be for star delta starting as this needs three contactors and a timer and as said the fourth one would be for some other function, such as a head cooling fan or something,
or, and this is what i was wondering,
If you mean contacts and not contactors, that is to say a four pole contactor where three are used for the three phase power to the comp and the fourth contact could be for many other things, it could be a normally closed contact so it is on when the comp is off, this would be for the crank case heater, or maybe its could be a normally open contact that opens the oil return solenoid when the comp is running.
There are many possibilities.
-
15-06-2010, 04:36 AM #7
Re: Auxillary Contactor
Hi Peter.
My post was based around the fact that in the feild self training is not the place to learn control systems and functions of components. With all the health and safety requirements, personal risk and public risk, the reality is do not do anything that you do not understand or are qualified to undertake technically. Simple instruction with an electrical drawing is far safer for everyone. Supervised instruction.
-
15-06-2010, 11:09 AM #8
Re: Auxillary Contactor
what the function of an auxillary contactor is?
A contactor is an electrically controlled switch used for switching a power or control circuit.
An additional motor starter contact used to provide memory to control circuits. When energized, the motor starter closes the auxiliary contact, maintaining a closed/open circuit depending upon normaly open & Normaly closed contact.
Try to understand the panel electrical ckt diagram.
Similar Threads
-
splattered points on contactor
By joe magee in forum Trouble ShootingReplies: 14Last Post: 10-06-2009, 06:04 PM -
Why a capacitor on contactor coil
By wambat in forum ElectricalReplies: 18Last Post: 15-05-2009, 03:18 AM -
Single pole contactor & crankcase heater
By herefishy in forum Air ConditioningReplies: 7Last Post: 01-04-2009, 08:38 AM -
SR2 50 models electric SBY diagonostics made simple
By absolute-zero in forum TransportReplies: 5Last Post: 04-01-2008, 05:11 PM -
Bad Contactor
By subzero*psia in forum Air ConditioningReplies: 8Last Post: 27-11-2001, 10:56 PM