    ship's reefer chamber



    hi guys, i seek technical advise for small capacity refrigeartion system. what is the minimum size for the compressor to have low temp application say -12 to -18 deg c. i got existing installation of +5 to 10 deg c but need to convert it to minus temp of -12 to -18 deg c. do i need to change the compressor, evaporator or just chage the expansion valve type or adjust the setting. im cluel]ess on this matter.thanks in advance. this is just use for provision on board the ship.



  2. #2
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: ship's reefer chamber

    is the room insulation thick enough to cope with the lower temperature,this is the first place to start before equipment selection
    mmm to beer or not to beer...........lets drink breakfast

  3. #3
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: ship's reefer chamber

    There is no "minimum size" for a compressor to pump low temps. Compressors are designed to run in a specific temperature range. Some do have a wide range of pumping ability, but not all of them.

    To determine if your compressor will pump a lower SST we need to know the model.
    Last edited by powell; 10-06-2010 at 04:17 AM.
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

  4. #4
    Join Date
    Sep 2009
    Location
    Australia
    Posts
    41
    Rep Power
    0

    Re: ship's reefer chamber

    as said above, you will need to check room insulation thickness, accumulator for comp, different LP cut out (if out of range), different insulation thickness for pipe lines, different TX if load is changing.........there are many other things you need to work out including room flooring, defrosting arrangements....etc gud luck
    BR

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Help cutting open 40ft reefer, we now have problems
    By adrian_uk17 in forum Industrial
    Replies: 50
    Last Post: 28-11-2010, 08:11 AM
  3. Reefer Tecnnichian Training
    By cnbrazil in forum Transport
    Replies: 4
    Last Post: 15-08-2009, 04:41 PM
  4. Replies: 10
    Last Post: 13-06-2008, 05:57 AM
  5. Humidity Chamber - Please Help
    By Deejay in forum Technical Discussions
    Replies: 4
    Last Post: 29-09-2007, 03:17 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •