    stuck on reversible ac system question in kotza book



    hi there,

    i am reading the kotza book which i am studying at home at night and have a question. i am reading about reversible A/C system so just a split system as the example is.

    it says in my book that the liquid reciever is used when systems have 4way reversing valves and that in cooling operation mode the condensor is full of liquid. this bit i understand.

    but then says when the cycle is reversed in to heat mode and the condensor changes in to an evap, this means a large quanity of liquid is being drawn into the compressor hence the liquid reciever being fitted to the suction side of the compressor.

    please could someone explain why large quantities of liquid would be in the Outdoor Unit which has then become the evap?

    i thought on heat mode that would mean the indoor unit would have the large quanity of liquid inside it.

    struggling to get my head around this bit?

    cheers lee



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: stuck on reversible ac system question in kotza book

    Firstly splits normally have a suction accumulator not a liquid receiver to protect the compressor.

    Now back to your headache...

    Think about the system in cooling when the evaporator is gas and the condenser is liquid; the gas is returning, via the reversing valve, through accumulator to the compressor.

    Now, when the unit changes over into heating mode it starts with the liquid in the outdoor coil; what was the condenser is now the evaporator. The liquid gets sucked, via the reversing valve and accumulator, into the compressor. The liquid is held in the accumulator with the gas being taken off the top to the compressor.

    Once the system has stabilised the liquid has relocated to the indoor, condenser, coil and the evaporator is feeding gas back to the compressor.

    If you now change back to cooling the liquid has now got to be moved back to the outdoor coil so it will go via the accumulator again.

    Clear as mud now?
    Last edited by Brian_UK; 09-06-2010 at 11:14 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: stuck on reversible ac system question in kotza book

    hi brian
    thats great that i understand now the book is not being clear for me, so on startup from a mode change ie cooling to heating this would mean the liquid gets sucked back towards the compressor then when the cycle is working how it should the liquid will then be in the indoor unit on heating.

    i am on the right track now aint i mate?

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: stuck on reversible ac system question in kotza book

    That's it, you've got it.

    Cooling: Wet outside/dry inside
    Heating: Wet inside/dry outside.

    Simple graphics here...
    http://www.copper.org/applications/p...hrml_main.html
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  4. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 03:42 PM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •