Results 1 to 3 of 3
  1. #1
    koolbrez's Avatar
    koolbrez Guest

    High KW per ton on york 2k ton YK



    I suspect dirty tubes but could use some reassurance, My evaporator psi is higher than normal and my head psi is higher, any other sugestions?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: High KW per ton on york 2k ton YK

    Sounds like a fair assumption assuming that you are talking about the water pressures on the evaporator.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: High KW per ton on york 2k ton YK

    By evaporator psi do you mean the pressure diff across the evap or high suction pressure.
    If you mean both suction and discharge are higher pressures. Then check out your condensing unit.
    There could be an issue there?
    Grizzly

Similar Threads

  1. YORK YAEP HIGH DESCH ERROR...PLS Help
    By webdrops in forum Trouble Shooting
    Replies: 7
    Last Post: 15-06-2010, 06:39 PM
  2. Over charged system... what symptoms?
    By Clk320_Greg in forum Trouble Shooting
    Replies: 2
    Last Post: 19-10-2009, 06:25 PM
  3. York Chiller High Line Voltage Problem
    By shamyl in forum Electrical
    Replies: 5
    Last Post: 19-07-2009, 07:53 PM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •