    koolbrez's Avatar
    koolbrez Guest
    High KW per ton on york 2k ton YK
    I suspect dirty tubes but could use some reassurance, My evaporator psi is higher than normal and my head psi is higher, any other sugestions?
    11,025
    Re: High KW per ton on york 2k ton YK
    Sounds like a fair assumption assuming that you are talking about the water pressures on the evaporator.
    Somerset
    69
    4,697
    By evaporator psi do you mean the pressure diff across the evap or high suction pressure.
    If you mean both suction and discharge are higher pressures. Then check out your condensing unit.
    There could be an issue there?
  1. YORK YAEP HIGH DESCH ERROR...PLS Help
    By webdrops in forum Trouble Shooting
    Last Post: 15-06-2010, 06:39 PM
  2. Over charged system... what symptoms?
    By Clk320_Greg in forum Trouble Shooting
    Last Post: 19-10-2009, 06:25 PM
  3. York Chiller High Line Voltage Problem
    By shamyl in forum Electrical
    Last Post: 19-07-2009, 07:53 PM
  4. Compressor loading, cooling, and range of operation.