    daikin r22 vrf



    been to a site today. old r22 system e4 and u4 fault. found condensor off put on now faulting
    12v dc found being sent inside, this should be more.

    did a bit of searching and found out this system had recently had a fan coil removed. went to where the fan coil was and found 4 2core cables all connected

    this has a central controller on it. i am assuming there is an in and out on f1f2 and also 2 cable sgoing i assume a central controller.

    do i need to tell the outdoor unit there is one less indoor, do i need to adjust the central controller to tell it one has gone

    what do i need to do ta

    Rob

    oh and to top it off the twin split replacing the old indoor unit is over charged by approx 10 gilos. oh joy



  2. #2
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: daikin r22 vrf

    Is this an R22 G, H or K series? 2 pipe heat pump or 3 pipe heat recovery?
    G series are addressed by rotary switches.
    H & K series will auto address but centralised controller group addresses are programmed by indoor remote

  3. #3
    Join Date
    Aug 2005
    Location
    uk
    Age
    46
    Posts
    82
    Rep Power
    19

    Re: daikin r22 vrf

    all sorted now thanks tho, it was a 2 pipe system, addressed by a remote on a central controller no remotes

    where the old unit was removed the wires were wrongly connected and also the central controller was still looking for the missing cassette

    also looked at another split while on site, found it 12kg over charged, new install. it had an additional 16kg added on a 70m run!!!!!!!!!!!!!!!

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin FDYQ250M
    By carl in forum Air Conditioning
    Replies: 7
    Last Post: 11-08-2009, 12:56 AM
  3. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  4. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  5. Getting a price from Daikin....
    By monkey spanners in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 17-08-2008, 09:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •