    Refrigerant oil analysis



    Hi Chaps

    Technical assistance required for a British Refrigeration Engineer a little out of his depth

    We have 2 copeland scroll compressors on a chiller unit & would like to know if they have been damaged by moisture ingress.

    An oil analysis was carried out but I need help in interpreting the results

    Can anyone help?

    MACHINERY DESCRIPTION Compressor
    DATE SAMPLED 4/20/2010
    OIL GRADE / MAKE Emkarate Synthetic Polyolester RL32H

    TEST METHOD MEASUREMENT RESULT
    Kin. Visc. @ 40°C ASTM D445 mm2/s 27.8
    Kin. Visc. @ 40°C after degassing ASTM D445 mm2/s 29.46
    Water Content ASTM D95 %m/m 0
    Total Acid Number ASTM D974 mg KOH/g 0.09
    Strong Acid Number ASTM D974 mg KOH/g 0
    Total Acid Number with respect to Zinc Calculated mg KOH/g <0.01

    TEST PARTICLE COUNT
    METHOD PORE BLOCKAGE ISO 4406
    MEASUREMENT PARTICLES / 1ml OIL


    ELEMENTS IN PPM
    Wear Metals Contaminants Additives
    Iron 1
    Copper 0
    Lead 0
    Chromium 0
    Aluminium 58
    Molybdenum 0
    Tin 0
    Nickel 0
    Silicon 5
    Sodium 0
    Lithium 0
    Calcium 0
    Barium 0
    Magnesium 0
    Zinc 0
    Phosphorus 1
    Boron 1
    Potassium 0

    COMMENTS
    The oil condition is good.
    Aluminium wear is high but remaining levels are acceptable.
    There is no visible wear debris.

    This is on production equipment so reliability is important but I don't want to fork out £2000 per compressor on the off-chance that they are damaged.

    Mark Breward



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Refrigerant oil analysis

    What makes you think the compressors are damaged the Oil analysis seems fine. moisture in the system can give you carbon deposits on the scrolls have you had water ingrees in to the chiller if so a good long triple vac should sort it out.

  3. #3
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Refrigerant oil analysis

    Hi Mark

    Why do you think you have moisture in your system ?
    Is the lab that did your analysis familiar with refrigeration oils & systems ?

    Normally the lab should be able to explain any results & advise accordingly.
    All other lab results i've seen have given moisture content in ppm, which is normally advised to be less than 50ppm in a refrigeration system. Not sure if the scale that your lab uses would be this accurate. It gives water content as 0, it may be expected to see some level in a used system.
    Have been advised before that the TAN (Total Acid Number) for new oil is around 0.04 to 0.05..
    If no one else on the forum can help may be the oil or compressor manufacturers could give you some guidelines.
    Sometimes a high silicon level can be an indication that moisture saturated desiccant has started to break-up.

    Otherwise you could buy some new oil of the type you have & send some away for analysis. The results could then be used as a reference.
    Regular testing can show trends in oil & gas contamination before they get to dangerous levels.

    You could always just change the oil, although this may be pointless if any contamination in the system is not cleaned up..
    Last edited by Gingerair; 08-06-2010 at 05:59 PM. Reason: Sun spots...

  4. #4
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Refrigerant oil analysis

    make a regular change of filter/dryers.
    as long as the drawn Amps are in accepteble range, you don't have to worry. otherwise you can always call on a elektric engineer who has an strong megger or oscilloscoop to test the windings on damage.

    Ice

  5. #5
    Join Date
    Aug 2003
    Location
    London uk
    Posts
    23
    Rep Power
    0

    Re: Refrigerant oil analysis

    Thank you all for your help, I sent the oil analysis to the compressor manufacturer & got the following reply:

    Based on our interpretation of the report. The quantity of aluminum present on the oil sample is high.

    On the internal parts of the scroll model the motor and the oldham coupling are mostly built with this material. The function of the oldham coupling is to allow the rotational motion of the rotor/shaft assembly to be changed into a precise orbiting motion. Mostly the factors that can cause such problem for the coupling is when the compressor accumulates large quantity of liquid.

    The life span of the compressor may already be shortened if the oldham coupling is damaged. For this reason we can not commit if the compressor should still be used afterwards.

    Any comments would be appreciated

    Mark

  6. #6
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Refrigerant oil analysis

    Mostly the factors that can cause such problem for the coupling is when the compressor accumulates large quantity of liquid.
    By quantities of liquid they mean refrigerant as it does not compress in a liquid state this can seriously damage scrolls, personally i would recommision the system and see how it runs if the comps are damaged then replace them

  7. #7
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Refrigerant oil analysis

    Yep, could not agrey more. but wat was, or is the couse, that the comps are liquid succing?
    beware when yore going to replace them, and the problem still exists.

    Ice

  8. #8
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Refrigerant oil analysis

    +1, sounds like you're getting liquid back to the compressor. Just need to identify the reasons why now..

  9. #9
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Refrigerant oil analysis

    Dirty evap? fans broken on evap? ore overcharge, when its not enough cool, just ad some more...(LOL)

    Ice

  10. #10
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Refrigerant oil analysis

    Hi Mark

    Did you also check with the lab that did your analysis about the value they gave for the water content ?
    Not sure if the scale they've used is for water content per % mass.. It's needs to be acurate down to parts per million, ppm..

  11. #11
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Refrigerant oil analysis

    Not much to the analysis other than the aluminum. They did employ essentially Mineral Oil test and of course, this is a syntheitc....So anything on the strong acid no side represents a breakdown of the refrigerant, not carbonic acids as per water+ mineral oil +Temperature woudl make.

    Aluminum and Copeland's input both ineresting: barring the coupling and certain motor parts, and presuming the motor is the only source for particulate aluminum and not the evaporator coils or similar: appears the a liquid incident has overloaded the couping; whcih nominally means the scrolls have passed some aluminum fragments. The coupling is portion of the motor bearing arrangement so reduced life of the compressor unit is to be expected.



    And if this thing contains synthetic lube, TAN should be near-0 because mixing some of the new lubes with water doesn't make acidity...But

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  4. MHI FDCA400HKXRE4 Tech Info Please
    By L.JT in forum Trouble Shooting
    Replies: 5
    Last Post: 23-08-2008, 11:00 PM
  5. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •