14-04-2005, 07:16 PM #1
extreme temp cpnditions..
hi guy's
this was thrown to me today..i have some thoughts but...
temperature controlled switch room approx 3mx3mx3m.. 21 deg'c
'outdoor' conditions range + 60 deg 'c to -20 deg'c
whatcha fink??
cheers
richard
-
14-04-2005, 07:23 PM #2
Re: extreme temp conditions..
Where on earth you get 80°c temp difference?
You Can not survive such heat, So how can one service ac unit?
48°c was my maximum, it was hard to breath.
Chemi
-
14-04-2005, 07:24 PM #3
Re: extreme temp cpnditions..
Indoor conditions - no problems.
Outdoor conditions - well if the ambient temperature is above the condensing temperature of the refrigerant you won't get condensation taking place and bang goes your refrigeration circuit.
Unless you or Marc know of high temp refrigerants
-
14-04-2005, 07:34 PM #4
Re: extreme temp cpnditions..
Originally Posted by frank
well my mind drifts on to various options like a water cooled condenser water spray during the extreme..a cascade type -a mis matched system 10kw outdoor +7kw indoor etc
I know that the japanese splits are rated to near 50 deg'c and I know the middle east gets chilly at night sometimes
anyway keep expanding your thoughts..
cheers
richard
-
14-04-2005, 10:48 PM #5
Re: extreme temp cpnditions..
My first thought is this is not a UK spec is it ?
Is the condenser mounted under glass somewhere or are we back to the a/c in space question?
What are the chances of having additional cooling to the +60°C area to reduce that temperature ?
No. the more I think about it....where are you getting +60°C from ???Brian - Newton Abbot, Devon, UK
Retired March 2015
-
15-04-2005, 01:57 AM #6
Re: extreme temp cpnditions..
To handle the high ambient condition you will pretty well be stuck with R-134a as a refrigerant. I presume you you will have a heat load and have to operate the cooling system at the -20 dC ambient. The easiest way to handle this is to use condenser flooding and a heated and insulated receiver.
The unit controls will need to located in the cool space as the 60 dC ambient will cook an outdoor control panel.
Water is probably not an option, as most places that have such a high ambient, do not have the water to waste on an evaporative cooler.
You might consider a glycol cooling loop with a free cooler (air to glycol exchanger) for when the ambient drop low enough to shut down the compressor.
Ken
Similar Threads
-
MP66 & Compressor Overheating
By Intermez in forum Technical DiscussionsReplies: 111Last Post: 13-04-2010, 08:58 PM -
Air Source Heat Pump - temp of refrigerant leaving evaporator
By anup in forum FundamentalsReplies: 3Last Post: 06-11-2006, 05:04 AM -
Condensing temp in refrigeration
By anup in forum FundamentalsReplies: 1Last Post: 02-10-2005, 11:18 AM -
Multiplex For Low Temp and Medium Temp
By allanbaker in forum Technical DiscussionsReplies: 0Last Post: 28-11-2002, 10:15 AM -
Endless Freezer as Endless Cooler (10 door)
By herefishy in forum CommercialReplies: 95Last Post: 17-04-2002, 12:54 PM