    System requirements changing from R-22 to R-410A



    I have to design a new system using refrigerant R-410A instead of using R-22

    What would be the changes required???

    Plz even if you show me the right path i may be able to follow and get solution...

    Plz sir help me!!!

    I have to operate between temperature limits of 45 degree celsius (condenser) and 2 degree celsius (evaporator).

    Any type of help would be grateful

    Thanks in advance



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: System requirements changing from R-22 to R-410A

    Have you already designed an R22 unit ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2010
    Location
    India
    Age
    34
    Posts
    11
    Rep Power
    0

    Re: System requirements changing from R-22 to R-410A

    Quote Originally Posted by Brian_UK View Post
    Have you already designed an R22 unit ?
    we were using R-22 unit for many years (5-8)

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: System requirements changing from R-22 to R-410A

    Use the appropriate components suitable for the higher pressures.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: System requirements changing from R-22 to R-410A

    Tube Size could be one step lower than R22 but wall thickness should be higher.

  6. #6
    Join Date
    Jun 2010
    Location
    India
    Age
    34
    Posts
    11
    Rep Power
    0

    Re: System requirements changing from R-22 to R-410A

    Quote Originally Posted by sendhilkmar View Post
    Tube Size could be one step lower than R22 but wall thickness should be higher.
    sendhilkmar,

    thanks for the info.

    i know that the system pressures of r-410A is 50-60% higher than the R-22 and its latent heat capacity is also higher than r-22 because of which u gave me that suggestion.

    But instead of using a thicker and smaller dia pipe for connections if i use the thinner ones but of larger dia. will it pose me any difficulty???

    waiting for reply

    thanks in advance!!!!

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: System requirements changing from R-22 to R-410A

    Pipe must be suitable for the refrigerant being used regardless of size.

    What sort of systems are you designing?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Jun 2010
    Location
    India
    Age
    34
    Posts
    11
    Rep Power
    0

    Re: System requirements changing from R-22 to R-410A

    Quote Originally Posted by Brian_UK View Post
    Pipe must be suitable for the refrigerant being used regardless of size.

    What sort of systems are you designing?
    water chiller

  9. #9
    Join Date
    Jul 2008
    Location
    Singapore & Malaysia
    Age
    77
    Posts
    30
    Rep Power
    0

    Re: System requirements changing from R-22 to R-410A

    Recently I have inspected by Eddy Current Tubing Examination on "York" Chiller Mode: YSCBCAS35CD D on the Condenser and Evaporator Enhanced Copper tube.
    The Evaporator tube size OD 3/4" diam x 1.75 mm wall thickness and under the fins wall thickness 1.25 mm wall thickness.
    The Condenser tube size OD 3/4" diam x 2.11 mm wall thickness and under the fins wall thickness 1.5 mm wall thickness.
    The refrigerator use 132b.
    Hope this will help you on the design.

  10. #10
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    412
    Rep Power
    22

    Re: System requirements changing from R-22 to R-410A

    Quote Originally Posted by rickyccong View Post
    Recently I have inspected by Eddy Current Tubing Examination on "York" Chiller Mode: YSCBCAS35CD D on the Condenser and Evaporator Enhanced Copper tube.
    The Evaporator tube size OD 3/4" diam x 1.75 mm wall thickness and under the fins wall thickness 1.25 mm wall thickness.
    The Condenser tube size OD 3/4" diam x 2.11 mm wall thickness and under the fins wall thickness 1.5 mm wall thickness.
    The refrigerator use 132b.
    Hope this will help you on the design.
    can you please explain eddycurrent test method.
    moideen

  11. #11
    Join Date
    Jun 2010
    Location
    India
    Age
    34
    Posts
    11
    Rep Power
    0

    Re: System requirements changing from R-22 to R-410A

    Quote Originally Posted by rickyccong View Post
    Recently I have inspected by Eddy Current Tubing Examination on "York" Chiller Mode: YSCBCAS35CD D on the Condenser and Evaporator Enhanced Copper tube.
    The Evaporator tube size OD 3/4" diam x 1.75 mm wall thickness and under the fins wall thickness 1.25 mm wall thickness.
    The Condenser tube size OD 3/4" diam x 2.11 mm wall thickness and under the fins wall thickness 1.5 mm wall thickness.
    The refrigerator use 132b.
    Hope this will help you on the design.
    Thank u for ur info

Similar Threads

  1. Residential R-22 system. HO added 134a
    By Magnapro in forum Technical Discussions
    Replies: 5
    Last Post: 26-05-2010, 09:12 PM
  2. Enthalpy Increasing Buffer System
    By Reflexive in forum Technical Speculations
    Replies: 3
    Last Post: 23-12-2008, 03:18 PM
  3. Refrigeration system simulation and optimization
    By autt in forum System Optimization
    Replies: 7
    Last Post: 05-12-2008, 02:59 PM
  4. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 03:42 PM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •