08-06-2010, 05:28 AM #1
Refrigerants
Which refrigerant is better R404A or R134A for Blast Freezer application?
BR
-
08-06-2010, 09:42 PM #2
Re: Refrigerants
Dear GBRD,
In generaly refrigeration system for Blast Freezer is system with low temperature as -30...-40C, and in the past R404 is used only for low temperature, so if you need -40 - you should use R404.
The boiling point at atmospheric pressure for R404 is -46,7ºC, and the boiling point at atmospheric pressure for R134 is -26,4ºC, so if you want below -26,4ºC you will have vakuum in system and you will have air after some times.
Sorry for my bad English.
-
09-06-2010, 01:07 AM #3
Re: Refrigerants
Thank you PVA......your english is actually good.
BR
-
09-06-2010, 05:48 AM #4
-
09-08-2010, 11:10 AM #5
Re: Refrigerants
To moideen>>>>
Thanks for your complement and correction!
-
29-08-2010, 11:47 AM #6
Re: Refrigerants
Yes thats the big factor air and the Head pressure is the second. Make sure that the Kw r heat transfer of the condenser is correct for the compressor and cooling kw r of the plant so that u do not struggle with hi discharge temperature on the compressor's heads and to hi liquid temperature after the conversion. Also make sure with the compressor manufacturer that the compressor's suction and discharge valve plates can cope with the gas ( port size of the valve's) to prevent valve plate failure,and carbonizing of compressor oils.
Similar Threads
-
CARE refigerants by BOC
By dogma in forum RefrigerantsReplies: 8Last Post: 23-03-2010, 12:39 PM -
Are there standard-systems for natural refrigerants?
By Moeller in forum RefrigerantsReplies: 9Last Post: 25-05-2009, 10:01 AM -
Refrigerants and The Environment
By Josip in forum RefrigerantsReplies: 18Last Post: 18-12-2008, 05:53 PM -
Hydrocarbon refrigerants
By mbeychok in forum RefrigerantsReplies: 15Last Post: 01-09-2006, 10:03 PM -
TAXES on Refrigerants
By Argus in forum Legal-Business-MarketingReplies: 0Last Post: 16-04-2006, 12:49 PM