Thread: Refrigerants
    Sep 2009
    Australia
    41
    Refrigerants
    Which refrigerant is better R404A or R134A for Blast Freezer application?
    BR
    Ukraine
    Re: Refrigerants
    Quote Originally Posted by GBRD View Post
    Dear GBRD,
    In generaly refrigeration system for Blast Freezer is system with low temperature as -30...-40C, and in the past R404 is used only for low temperature, so if you need -40 - you should use R404.
    The boiling point at atmospheric pressure for R404 is -46,7ºC, and the boiling point at atmospheric pressure for R134 is -26,4ºC, so if you want below -26,4ºC you will have vakuum in system and you will have air after some times.
    Sorry for my bad English.
    Sep 2009
    Australia
    41
    Re: Refrigerants
    Thank you PVA......your english is actually good.
    BR
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2008
    u.a.e
    49
    412
    23
    Re: Refrigerants
    Quote Originally Posted by PVA View Post
    Dear GBRD,
    hi pva,you are correct, at present R404a is excellent for ultra low temperature applications.r-134a is not recommended for use in systems where the saturated suction temperature is below-10f.
    moideen-dubai
    Ukraine
    Re: Refrigerants
    To moideen>>>>
    Thanks for your complement and correction!
    Apr 2009
    South Africa
    49
    108
    Re: Refrigerants
    Dear GBRD,
    IThe boiling point at atmospheric pressure for R404 is -46,7ºC, and the boiling point at atmospheric pressure for R134 is -26,4ºC, so if you want below -26,4ºC you will have vakuum in system and you will have air after some times.
    Yes thats the big factor air and the Head pressure is the second. Make sure that the Kw r heat transfer of the condenser is correct for the compressor and cooling kw r of the plant so that u do not struggle with hi discharge temperature on the compressor's heads and to hi liquid temperature after the conversion. Also make sure with the compressor manufacturer that the compressor's suction and discharge valve plates can cope with the gas ( port size of the valve's) to prevent valve plate failure,and carbonizing of compressor oils.
  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Last Post: 23-03-2010, 12:39 PM
  2. Are there standard-systems for natural refrigerants?
    By Moeller in forum Refrigerants
    Last Post: 25-05-2009, 10:01 AM
  3. Refrigerants and The Environment
    By Josip in forum Refrigerants
    Last Post: 18-12-2008, 05:53 PM
  4. Hydrocarbon refrigerants
    By mbeychok in forum Refrigerants
    Last Post: 01-09-2006, 10:03 PM
  5. TAXES on Refrigerants
    By Argus in forum Legal-Business-Marketing
    Last Post: 16-04-2006, 12:49 PM