    Pulling a VAC!!!



    What happens when a vac is not properly pulled?
    I noticed that my helper was using the 3/8 hose on the manifold and forgot to cap the other port on the vac when we got to the second job. Can I suck the Ref (410A) back into the compressor and pull a Vac or is the Ref (410A) contaminated?? The unit was running a little high but it was condensing a lot.
    What should I do???



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pulling a VAC!!!

    When you don't evacuate as it should be done, you introducing moisture from air in system and non-condensable gases.
    Non-condensables take space in condenser and effectively reduces portion of condenser which reject heat. That mean you have high condensing temperatures/pressures and condenser cannot reject effectively all heat which is absorbed in refrigeration cycle.
    Moisture in R410 system bonds with high hygroscopic oil and create acids which damages compressor motor insulation and metal parts. Also, unabsorbed moisture could freeze in low temperature parts of system and clog capillary or TXV.
    You need to recover refrigerant, discard it, install combined filter dryer for de-humidification and de-acidification of oil and charge new fresh refrigerant after evacuation to 400-500 microns of vacuum.
    If your helper used micron gauge in first time, that would not happen.
    Last edited by nike123; 08-06-2010 at 06:58 AM.

  3. #3
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: Pulling a VAC!!!

    There is also a way to separate non condensables from the refrigerant. You will have to discard part of the refrigerant, but not all of it. Firstly you need to recover and recycle the 410A in a cylinder. Then, there is a method to separate both. After this treatment, the refrigerant can be reused.

    Anyway, as Nike123 said, the major problem remains in the circuit, as you have contaminated it with moisture, that will damage the oil, and create acid. You definitely need to clean properly the circuit. I am sorry to say that placing filter dryers does not remove the acidity.

    If you want to know how to separate the air from the refrigerant, just let me know.

    Regards,

    Nando

  4. #4
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Pulling a VAC!!!

    there are plenty of decent fridge firms in your local phone directory

Similar Threads

  1. Replies: 6
    Last Post: 09-06-2010, 05:13 PM
  2. Pulling faster vacuums
    By Aranon in forum Fundamentals
    Replies: 31
    Last Post: 04-09-2009, 07:32 PM
  3. Mitsubisi problem in pulling down temperature
    By teguh in forum Transport
    Replies: 8
    Last Post: 21-08-2009, 05:36 AM
  4. Vacuum pump not pulling good suction
    By marinechiller in forum Trouble Shooting
    Replies: 5
    Last Post: 15-07-2009, 10:27 PM
  5. Freezer not pulling down to Temp
    By ferret82 in forum Commercial
    Replies: 5
    Last Post: 23-03-2009, 10:59 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •