    thermostatic Expansion valve location



    I have cold store -40 C and 2 evaporators feed by thermostatic Expansion valve each one my question
    which you prefer put Expansion valve near evaporator in cold store -40 C or far from evaporator about 2 meters out the cold store +30 C


    Thank for help



  2. #2
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: thermostatic Expansion valve location

    TEV must situated near the evaporator...Why do you want to install it far from evaporator?
    Check:
    http://www.refrigeration-engineer.co...ad.php?t=23692
    In some places will have to think ...

  3. #3
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: thermostatic Expansion valve location

    In -40 your suction pressure is low and to get good result of TEV to sense of suction temperature it better you put near Evaporator

  4. #4
    Join Date
    Mar 2007
    Location
    Egypt
    Age
    55
    Posts
    54
    Rep Power
    18

    Re: thermostatic Expansion valve location

    [quote=Aik;190754]TEV must situated near the evaporator...Why do you want to install it far from evaporator?

    thank you for help
    I do not want to install it far from Evaporator it already install far from evaporator now iwant to re-install it correctly near evaporator is that the best?

  5. #5
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: thermostatic Expansion valve location

    Without any doubts...
    In some places will have to think ...

  6. #6
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: thermostatic Expansion valve location

    It depends, on evaporators that need a hoist to access it can be better to mount the TEV externally to the room to allow for service access, the last room i fitted i placed the valve on the roof with no issues, realistically you're only extending the pipe inlet by less than a meter.

    alec

  7. #7
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: thermostatic Expansion valve location

    .

    Outside the room, on the roof will ease the repairs and maint of the TEV in the system.

    If the pipes are correctly lagged then the differance between inside and outside will be minimal.

    If the sytem is working ok as it is then leave it.

    Coolroonings.

    .

  8. #8
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: thermostatic Expansion valve location

    have seen many a valve mounted on outside of room, as long as the pipes are well insulated as well as the valve i dont see any problem.

  9. #9
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: thermostatic Expansion valve location

    Hi there,

    If your TEv is MOP type then the valve head must be warmer than the bulb. To put the valve outside creates this temperature difference.
    What I do is : I use drain heaters (like cable) on top of the valve head.

    Cheers
    Even Einstein Asked Questions

  10. #10
    wendecai's Avatar
    wendecai Guest

    Re: thermostatic Expansion valve location

    Can anyone tell me ,what is the difference between Txv with Mop and Txv with Mop?

  11. #11
    Join Date
    Jan 2009
    Location
    Australia
    Age
    60
    Posts
    108
    Rep Power
    16

    Re: thermostatic Expansion valve location

    That's an easy one. They are both the same.

    The penalty with moving the valve upstream of the evaporator is the extra pressure drop in the line between the valve and the evaporator. That line effectively becomes an extension of the evaporator. Provided this extra pressure drop is accounted for and the line external to the room is insulated (you don't want to be wasting power trying to cool the world) it should work ok.

  12. #12
    Join Date
    Jan 2010
    Location
    Christchurch
    Age
    54
    Posts
    28
    Rep Power
    0

    Re: thermostatic Expansion valve location

    MOP = maximum operating pressure, basically the valve will operate like a crankcase pressure regulator and will not allow the suction pressure to raise above its "MOP", this can cause some problems during start up and pull down like in a blast freezer after a defrost, the suction pressure will remain constant untill the air temp/suction pressure drops, it helps the compressor get hold of the load without tripping on amps etc

Similar Threads

  1. Lg mps system ( expansion valve location)
    By hussain2002cab in forum Air Conditioning
    Replies: 6
    Last Post: 18-03-2010, 10:19 PM
  2. thermostatic expansion valve
    By ateeq.baig in forum Commercial
    Replies: 11
    Last Post: 03-06-2009, 05:05 PM
  3. thermostatic expansion valve sizing
    By ank_gl in forum Air Conditioning
    Replies: 2
    Last Post: 03-03-2009, 03:22 PM
  4. Thermostatic Expansion Valve TXV - Block Type
    By AastroGuru in forum Fundamentals
    Replies: 10
    Last Post: 24-12-2008, 09:53 AM
  5. location of the expansion valve
    By smpsmp45 in forum NH3
    Replies: 5
    Last Post: 28-09-2007, 11:00 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •