I have cold store -40 C and 2 evaporators feed by thermostatic Expansion valve each one my question
which you prefer put Expansion valve near evaporator in cold store -40 C or far from evaporator about 2 meters out the cold store +30 C
Thank for help
-
07-06-2010, 06:15 PM #2
Re: thermostatic Expansion valve location
TEV must situated near the evaporator...Why do you want to install it far from evaporator?
Check:
http://www.refrigeration-engineer.co...ad.php?t=23692In some places will have to think ...
-
07-06-2010, 06:43 PM #3
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Re: thermostatic Expansion valve location
In -40 your suction pressure is low and to get good result of TEV to sense of suction temperature it better you put near Evaporator
-
07-06-2010, 06:45 PM #4
Re: thermostatic Expansion valve location
[quote=Aik;190754]TEV must situated near the evaporator...Why do you want to install it far from evaporator?
thank you for help
I do not want to install it far from Evaporator it already install far from evaporator now iwant to re-install it correctly near evaporator is that the best?
-
07-06-2010, 08:11 PM #5
Re: thermostatic Expansion valve location
Without any doubts...
In some places will have to think ...
-
07-06-2010, 08:28 PM #6
Re: thermostatic Expansion valve location
It depends, on evaporators that need a hoist to access it can be better to mount the TEV externally to the room to allow for service access, the last room i fitted i placed the valve on the roof with no issues, realistically you're only extending the pipe inlet by less than a meter.
alec
-
07-06-2010, 08:45 PM #7
Re: thermostatic Expansion valve location
.
Outside the room, on the roof will ease the repairs and maint of the TEV in the system.
If the pipes are correctly lagged then the differance between inside and outside will be minimal.
If the sytem is working ok as it is then leave it.
Coolroonings.
.
-
07-06-2010, 08:58 PM #8
Re: thermostatic Expansion valve location
have seen many a valve mounted on outside of room, as long as the pipes are well insulated as well as the valve i dont see any problem.
-
09-06-2010, 07:55 AM #9
Re: thermostatic Expansion valve location
Hi there,
If your TEv is MOP type then the valve head must be warmer than the bulb. To put the valve outside creates this temperature difference.
What I do is : I use drain heaters (like cable) on top of the valve head.
CheersEven Einstein Asked Questions
-
04-07-2010, 09:48 PM #10
Re: thermostatic Expansion valve location
Can anyone tell me ,what is the difference between Txv with Mop and Txv with Mop?
-
04-07-2010, 10:31 PM #11
Re: thermostatic Expansion valve location
That's an easy one. They are both the same.
The penalty with moving the valve upstream of the evaporator is the extra pressure drop in the line between the valve and the evaporator. That line effectively becomes an extension of the evaporator. Provided this extra pressure drop is accounted for and the line external to the room is insulated (you don't want to be wasting power trying to cool the world) it should work ok.
-
05-07-2010, 03:26 AM #12
Re: thermostatic Expansion valve location
MOP = maximum operating pressure, basically the valve will operate like a crankcase pressure regulator and will not allow the suction pressure to raise above its "MOP", this can cause some problems during start up and pull down like in a blast freezer after a defrost, the suction pressure will remain constant untill the air temp/suction pressure drops, it helps the compressor get hold of the load without tripping on amps etc
Similar Threads
-
Lg mps system ( expansion valve location)
By hussain2002cab in forum Air ConditioningReplies: 6Last Post: 18-03-2010, 10:19 PM -
thermostatic expansion valve
By ateeq.baig in forum CommercialReplies: 11Last Post: 03-06-2009, 05:05 PM -
thermostatic expansion valve sizing
By ank_gl in forum Air ConditioningReplies: 2Last Post: 03-03-2009, 03:22 PM -
Thermostatic Expansion Valve TXV - Block Type
By AastroGuru in forum FundamentalsReplies: 10Last Post: 24-12-2008, 09:53 AM -
location of the expansion valve
By smpsmp45 in forum NH3Replies: 5Last Post: 28-09-2007, 11:00 AM