07-06-2010, 03:41 PM #1
30000btu split
Hi All
having a bit of a problem with a 30000 btu split unit.
the unit runs fine in cooling mode, but when i switch over to heating, nothing happens. the indoor fan does not start. the outside fan runs, the pipes on the outer don't even get hot. i change the reverse valve because i though it was stuck, but still nothing? i leave the unit running for 10 mins & inside fan still not comming on? gas pressure is good, no problem there, +/- 3,5 bar on the low. when on heating it sits at +/-4-5 bar? any ideas?
-
07-06-2010, 04:48 PM #2
Re: 30000btu split
hi draco, did you reset the controls to a new colder set point? did you give it time to come back on ? is it a heat pump?
-
08-06-2010, 09:14 AM #3
Re: 30000btu split
Unit works good in cooling mode, have no problems there. Heating is the problem, i added a bit more gas, the unit got too 10 bar, but still the inside fan never came on & the unit is stll not heating, i'm going to proceed to add more gas to the system, to see if i get the desired outcome.
-
08-06-2010, 09:31 AM #4
Re: 30000btu split
It's like the unit doesn't want to take in gas, on cooling it is sitting on 3.5 bar, low side. when i switch the unit off, the gauge only rises to 6 bars on the low.
-
08-06-2010, 11:57 AM #5
Re: 30000btu split
why ow why ore you adding more gas ? when in the first place it MIGHT have too much gas in it to start with ?
-
08-06-2010, 01:24 PM #6
Re: 30000btu split
supply mannual say's to add, till pressure is about 4.5 bars on the low side, as stated cooling is perfect. But this also does not work, unit increases pressure gradually to 30 bar & trips out. indoorfan still does not come on. evacuated system, checked capillary for blockage, none. time to start from scratch & regas slowly, will gas up to 3.5 bar on low again & test the heat function. could this be a sensor problem on the indoor?
-
08-06-2010, 02:04 PM #7
Re: 30000btu split
hi draco, I see its a new unit, its never run on heating , is the system pre- wired ¿ or is iot hard wiered ? if it is I would cheak the wiring, is the 3way valve energising < changing heating to cooling?< best of luck,
-
09-06-2010, 07:36 AM #8
Re: 30000btu split
Hi Sedgy, wiring is correct, 1 to 1, 2 to 2 etc. can only get up to 3 bars on cooling at the moment, is a cold day & gassing taking long, while heating up the bottle. only other thing i can think of is indoor sensor or cpu problem? compressor runs.
-
09-06-2010, 09:34 AM #9
Re: 30000btu split
If compressor starting in heating mode, check temperature gas pipe. If temperature is low that indoor unit fan be STOP.
-
14-06-2010, 06:59 AM #10
Re: 30000btu split
Compressor starts, pipe is luke warm & does not get hot. Indoor fan does not come on at all, outside fan works constantly, pressure rises to +/- 30 bars & unit trips out.
-
14-06-2010, 07:18 AM #11
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: 30000btu split
What is unit make and model#? What refrigerant?
Remove all gas and charge by weight stated on nameplate!!!! Do not charge it by pressure. If that is what is said in manual, then burn that manual.
Indoor fan is switched ON only after indoor heat exchanger probe is signaling that temperature of indoor heat exchanger is above 35°C (or somewhere near that figure) to prevent cold air blowing. If that sensor is faulty, fan will never going to start and you will newer charge that unit right by measuring pressures (even if it is good, you still will not charge it right by measuring only pressures).Last edited by nike123; 14-06-2010 at 07:22 AM.
-
14-06-2010, 09:18 AM #12
Re: 30000btu split
I have charged by weight, R22 model: Fairland, the pipes do not get hot enough, i have changed the sensor & cpu on the unit, still nothing for heating & i have changed the 3way valve, checked capillaries for blockages, all ok, at a loss here.
-
14-06-2010, 09:38 AM #13
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Similar Threads
-
Fujitsu Split System Outdoor Fan Wiring Issue
By damo_666 in forum Air ConditioningReplies: 3Last Post: 29-03-2010, 03:04 AM -
How good is your split system running?
By acnerd in forum Air ConditioningReplies: 18Last Post: 05-08-2009, 07:35 PM -
Sensible Heat Factor / capacity of Inverter split Systems at part load?
By Greengrocer in forum Technical SpeculationsReplies: 31Last Post: 09-02-2009, 04:57 PM -
Australian split installers, some info needed
By paul_h in forum Air ConditioningReplies: 10Last Post: 20-05-2008, 03:40 PM -
Do you beleive in data of split units?
By jirhol in forum FundamentalsReplies: 4Last Post: 29-03-2008, 11:17 PM