    30000btu split



    Hi All

    having a bit of a problem with a 30000 btu split unit.
    the unit runs fine in cooling mode, but when i switch over to heating, nothing happens. the indoor fan does not start. the outside fan runs, the pipes on the outer don't even get hot. i change the reverse valve because i though it was stuck, but still nothing? i leave the unit running for 10 mins & inside fan still not comming on? gas pressure is good, no problem there, +/- 3,5 bar on the low. when on heating it sits at +/-4-5 bar? any ideas?



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: 30000btu split

    hi draco, did you reset the controls to a new colder set point? did you give it time to come back on ? is it a heat pump?

  3. #3
    Join Date
    Sep 2009
    Location
    Gauteng
    Age
    51
    Posts
    16
    Rep Power
    0

    Re: 30000btu split

    Unit works good in cooling mode, have no problems there. Heating is the problem, i added a bit more gas, the unit got too 10 bar, but still the inside fan never came on & the unit is stll not heating, i'm going to proceed to add more gas to the system, to see if i get the desired outcome.

  4. #4
    Join Date
    Sep 2009
    Location
    Gauteng
    Age
    51
    Posts
    16
    Rep Power
    0

    Re: 30000btu split

    It's like the unit doesn't want to take in gas, on cooling it is sitting on 3.5 bar, low side. when i switch the unit off, the gauge only rises to 6 bars on the low.

  5. #5
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: 30000btu split

    why ow why ore you adding more gas ? when in the first place it MIGHT have too much gas in it to start with ?

  6. #6
    Join Date
    Sep 2009
    Location
    Gauteng
    Age
    51
    Posts
    16
    Rep Power
    0

    Re: 30000btu split

    supply mannual say's to add, till pressure is about 4.5 bars on the low side, as stated cooling is perfect. But this also does not work, unit increases pressure gradually to 30 bar & trips out. indoorfan still does not come on. evacuated system, checked capillary for blockage, none. time to start from scratch & regas slowly, will gas up to 3.5 bar on low again & test the heat function. could this be a sensor problem on the indoor?

  7. #7
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: 30000btu split

    hi draco, I see its a new unit, its never run on heating , is the system pre- wired ¿ or is iot hard wiered ? if it is I would cheak the wiring, is the 3way valve energising < changing heating to cooling?< best of luck,

  8. #8
    Join Date
    Sep 2009
    Location
    Gauteng
    Age
    51
    Posts
    16
    Rep Power
    0

    Re: 30000btu split

    Hi Sedgy, wiring is correct, 1 to 1, 2 to 2 etc. can only get up to 3 bars on cooling at the moment, is a cold day & gassing taking long, while heating up the bottle. only other thing i can think of is indoor sensor or cpu problem? compressor runs.

  9. #9
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: 30000btu split

    If compressor starting in heating mode, check temperature gas pipe. If temperature is low that indoor unit fan be STOP.

  10. #10
    Join Date
    Sep 2009
    Location
    Gauteng
    Age
    51
    Posts
    16
    Rep Power
    0

    Re: 30000btu split

    Compressor starts, pipe is luke warm & does not get hot. Indoor fan does not come on at all, outside fan works constantly, pressure rises to +/- 30 bars & unit trips out.

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 30000btu split

    What is unit make and model#? What refrigerant?
    Remove all gas and charge by weight stated on nameplate!!!! Do not charge it by pressure. If that is what is said in manual, then burn that manual.
    Indoor fan is switched ON only after indoor heat exchanger probe is signaling that temperature of indoor heat exchanger is above 35°C (or somewhere near that figure) to prevent cold air blowing. If that sensor is faulty, fan will never going to start and you will newer charge that unit right by measuring pressures (even if it is good, you still will not charge it right by measuring only pressures).
    Last edited by nike123; 14-06-2010 at 07:22 AM.

  12. #12
    Join Date
    Sep 2009
    Location
    Gauteng
    Age
    51
    Posts
    16
    Rep Power
    0

    Re: 30000btu split

    I have charged by weight, R22 model: Fairland, the pipes do not get hot enough, i have changed the sensor & cpu on the unit, still nothing for heating & i have changed the 3way valve, checked capillaries for blockages, all ok, at a loss here.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 30000btu split

    Quote Originally Posted by Draco View Post
    I have charged by weight, R22 model: Fairland, the pipes do not get hot enough, i have changed the sensor & cpu on the unit, still nothing for heating & i have changed the 3way valve, checked capillaries for blockages, all ok, at a loss here.

    Now measure pressure at heating mode and record line temperatures from compressor to indoor unit and to outdoor unit at entrance and exit of each element along discharge and liquid line.

Similar Threads

  1. Fujitsu Split System Outdoor Fan Wiring Issue
    By damo_666 in forum Air Conditioning
    Replies: 3
    Last Post: 29-03-2010, 03:04 AM
  2. How good is your split system running?
    By acnerd in forum Air Conditioning
    Replies: 18
    Last Post: 05-08-2009, 07:35 PM
  3. Sensible Heat Factor / capacity of Inverter split Systems at part load?
    By Greengrocer in forum Technical Speculations
    Replies: 31
    Last Post: 09-02-2009, 04:57 PM
  4. Australian split installers, some info needed
    By paul_h in forum Air Conditioning
    Replies: 10
    Last Post: 20-05-2008, 03:40 PM
  5. Do you beleive in data of split units?
    By jirhol in forum Fundamentals
    Replies: 4
    Last Post: 29-03-2008, 11:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •