    Ammonia liquid carry over



    Hi All

    As i know screw compressors are resistant against liquid carry over,Is it true?

    Is there any comparison between reciprocating compressors and screw compressors against liquid pumping



  2. #2
    Join Date
    May 2009
    Location
    Sydney
    Posts
    73
    Rep Power
    15

    Re: Ammonia liquid carry over

    If liquid refrigerant is allowed to enter a screw compressor it will pump the liquid straight into the oil separator. This will then prevent the oil pump from supplying oil into the screw compressor. If liquid enters a recip compressor it will wash the oil out of the sump and may also break valves etc. I dont know of any compressor that will handle any substantial quantity of liquid and any refrigeration plant should be designed to prevent this from happening.

  3. #3
    Join Date
    Sep 2009
    Location
    Australia
    Posts
    41
    Rep Power
    0

    Re: Ammonia liquid carry over

    screw comp cannot tolerate liquid at all. screws may cease & comp will break down. receip comp can probably handle liquid if there are leaks around rings, but would break down eventually. liquid is incompressible anyway.
    BR

  4. #4
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: Ammonia liquid carry over

    Agree. No matter what type of refrigerant you are using, rotary screw comps. cannot handle incompressible liquid refrigerant instantly. Recip. comps. can handle only small amounts of liquid but it will not last and soon will lead to compressor damage.
    <"No one is so smart, they just stay with problems longer and use their imagination">

  5. #5
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Ammonia liquid carry over

    I have a different opinion.
    Screw compressors can handle some liquid. Some liquid will evaporate inside compressor because of compression heat and a lot of warm oil. The rest of liquid will go to oil separator and later it can lead to oil pressure drop and compressor will trip.
    Recip. compressors have only compression heat to fight the liquid. Major problem with recip. that they have discharge valves. These valves can't pass a lot of liquid and compressor can be blown. Screw compressors don't have discharge valves and they can handle more liquid than recip. However, they aren't liquid pumps.

  6. #6
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Ammonia liquid carry over

    Sergei has it right.

  7. #7
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: Ammonia liquid carry over

    Yes, it may be true that the screw compressor is less sensitive to slugging in comparison to the reciprocating type, but a slug of liquid refrigerant may vaporize and interrupt the flow of injected oil resulting in scored rotors. This is the cause of the loud "screeching" noise in screws during liquid flooding. Overhauling or worst, replacement of screw comps. is very costly.


    On liquid flooded start, recips. have crankcase oil heater ahead of comp. start-up which boils off any liquid present in the crankcase, but long term repeated slugging will also lead to comp. damage.

    Anyhow, it should be remembered that no compressor is designd to handle incompressible refrigerant liquid.
    Last edited by ref717; 09-06-2010 at 08:57 PM.
    <"No one is so smart, they just stay with problems longer and use their imagination">

  8. #8
    Sukhvinder's Avatar
    Sukhvinder Guest

    Post Re: Ammonia liquid carry over

    to avoid ammonia liquid use pump system to save compressor & time! no compressor can ressit liquid, in screw it get into oil sperator & in reciprocating (piston) can break valves, piston or more worse can break crank shaft!

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Ammonia liquid pump
    By jessica in forum NH3
    Replies: 19
    Last Post: 30-05-2008, 12:53 PM
  3. ammonia liquid
    By faryuki in forum NH3
    Replies: 5
    Last Post: 15-05-2007, 02:50 PM
  4. Liquid ammonia injection for cooling.
    By mrsparky in forum Industrial
    Replies: 91
    Last Post: 19-04-2007, 09:44 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •