    Time Consuming



    Working on a Hitachi multisplit system with a scroll compressor, normally holds 9kg of R407c and requires an additional 8kgs totalling 17kgs. Have charged one of these systems before bombing high side with liquid until no more will enter, then running the system and slowly feeding liquid into low side. My problem is it takes forever and initially cuts out thermal protection. Does anyone have a better method or recommend an instrument etc?



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Time Consuming

    hi ark, can you pump the system down?

  3. #3
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Time Consuming

    sedgy good idea

    Arc see function PUMP DOWN in service manual and return refrigerant into outdoor unit. Then vacuuming and
    add missing quantity of refrigerant in liquid pipe. Do not forget to close service valves on the outdoor unit after PUMP DOWN

  4. #4
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Time Consuming

    Arc That henceforth such was not, it is necessary to heat a cylinder

  5. #5
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Time Consuming

    134a in cold weather with cold bottles is worst...
    Use a reclaim unit to pump any extra charge into liquid line..
    Last edited by Gingerair; 06-06-2010 at 08:54 PM. Reason: Add 134a titbit..

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Time Consuming

    Connect your reclaim machine in push/pull mode and push the liquid into the system.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Time Consuming

    Arc Forget that I wrote.
    Reclaim machine use is a civilised way.

  8. #8
    Join Date
    Jul 2008
    Location
    Australia
    Age
    40
    Posts
    20
    Rep Power
    0

    Re: Time Consuming

    Pumping the system down is a good idea. Would like to throw the cylinder in a bottle of hot water but my bottles have to be inverted for liquid.
    Was going to pump it in with my reclaim but slightly reluctant about contamination. The gas I pulled from it was acidic, not sure if a drier on the end of it would do job?
    Also I seem to lose 200-300gms in the machine but this could be allowed for.
    I even called Mastercool who manufacture my recovery unit but there technical crew could not recommend/comment on it?

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. Normal compressor cycle time
    By Jim_H_WY in forum Trouble Shooting
    Replies: 7
    Last Post: 19-12-2009, 06:00 AM
  4. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  5. what do you do on your off time?
    By Tycho in forum Chit Chat & Service Stories
    Replies: 15
    Last Post: 09-10-2006, 12:03 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •