Time Consuming
Working on a Hitachi multisplit system with a scroll compressor, normally holds 9kg of R407c and requires an additional 8kgs totalling 17kgs. Have charged one of these systems before bombing high side with liquid until no more will enter, then running the system and slowly feeding liquid into low side. My problem is it takes forever and initially cuts out thermal protection. Does anyone have a better method or recommend an instrument etc?
-
06-06-2010, 07:06 PM #2
Re: Time Consuming
hi ark, can you pump the system down?
-
06-06-2010, 07:44 PM #3
Re: Time Consuming
sedgy good idea
Arc see function PUMP DOWN in service manual and return refrigerant into outdoor unit. Then vacuuming and
add missing quantity of refrigerant in liquid pipe. Do not forget to close service valves on the outdoor unit after PUMP DOWN
-
06-06-2010, 07:49 PM #4
Re: Time Consuming
Arc That henceforth such was not, it is necessary to heat a cylinder
-
06-06-2010, 08:48 PM #5
Re: Time Consuming
134a in cold weather with cold bottles is worst...
Use a reclaim unit to pump any extra charge into liquid line..Last edited by Gingerair; 06-06-2010 at 08:54 PM. Reason: Add 134a titbit..
-
06-06-2010, 10:10 PM #6
Re: Time Consuming
Connect your reclaim machine in push/pull mode and push the liquid into the system.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
07-06-2010, 09:20 AM #7
Re: Time Consuming
Arc Forget that I wrote.
Reclaim machine use is a civilised way.
-
08-06-2010, 06:19 PM #8
Re: Time Consuming
Pumping the system down is a good idea. Would like to throw the cylinder in a bottle of hot water but my bottles have to be inverted for liquid.
Was going to pump it in with my reclaim but slightly reluctant about contamination. The gas I pulled from it was acidic, not sure if a drier on the end of it would do job?
Also I seem to lose 200-300gms in the machine but this could be allowed for.
I even called Mastercool who manufacture my recovery unit but there technical crew could not recommend/comment on it?
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Leak Testing?
By Thana in forum Trouble ShootingReplies: 36Last Post: 31-08-2010, 02:57 PM -
Normal compressor cycle time
By Jim_H_WY in forum Trouble ShootingReplies: 7Last Post: 19-12-2009, 06:00 AM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM -
what do you do on your off time?
By Tycho in forum Chit Chat & Service StoriesReplies: 15Last Post: 09-10-2006, 12:03 AM