    Trouble shoot Daikin Controller



    I have one BRC1D71 remote controller attached to four FXSQ indoor units with a VRV-S system. Attempts to change the indoor fan speed at the controller, whether using the fan speed button to change all indoor units or attempts to set an individual indoor unit by using service mode 44, do not work.

    While it seems like the controller is bad, is there way to trouble shoot it to make sure?

    Thank you.



  2. #2
    Join Date
    Mar 2010
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: Trouble shoot Daikin Controller

    Hi,

    Can you confirm the full model numbers of the indoor units:

    FXSQ - M or FXSQ - P

    M Series indoor units have multi tap fan motors, P Series have inverter driven motors. P Series indoor units require additional set up for static pressure.

    If you push the fan speed button, does the symbol change to show the change. Please advise and I may be able to help further

  3. #3
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Trouble shoot Daikin Controller

    Quote Originally Posted by Mentallist View Post
    Hi,

    Can you confirm the full model numbers of the indoor units:

    FXSQ - M or FXSQ - P

    M Series indoor units have multi tap fan motors, P Series have inverter driven motors. P Series indoor units require additional set up for static pressure.

    If you push the fan speed button, does the symbol change to show the change. Please advise and I may be able to help further
    Mentallist,

    Thank you for your response. The indoor units are the M series.

    When attempting to change fan speed for all indoor units with the controller using the fan speed button, the symbol does change on the controller but the actual fan speed does not change with any of the indoor units.

    When attempting to change fan speed through service code 44 there is no change (from 1 to 3 or such) showing on the controller and the fan speed does not change.

    Hope that helps to clarify.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Trouble shoot Daikin Controller

    If I remember correctly, service level 40 is for monitoring not setting
    Last edited by frank; 11-06-2010 at 08:54 PM.

  5. #5
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Trouble shoot Daikin Controller

    Quote Originally Posted by frank View Post
    Of I remember correctly, service level 40 is for monitoring not setting
    frank, You may well know better than I but it looks like service codes 43, 44, and 45 allow making settings. Service code 44 allows for setting individual indoor unit unit blower speed and air flow direction for ductless units.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Trouble shoot Daikin Controller

    I'll check when next in the office on Monday

  7. #7
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Trouble shoot Daikin Controller

    Quote Originally Posted by frank View Post
    I'll check when next in the office on Monday
    Many thanks. Any info is helpful. I have attached the page form the service manual detail the various 40 codes.
    Attached Files Attached Files
    Last edited by mchild; 11-06-2010 at 09:00 PM.

  8. #8
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Trouble shoot Daikin Controller

    Quote Originally Posted by frank View Post
    I'll check when next in the office on Monday
    frank, Hoping you had a chance to check things on this issue at the office today. Thanks
    Last edited by mchild; 14-06-2010 at 07:32 PM.

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Trouble shoot Daikin Controller

    Unfortunately not. Had several things going on today which were unexpected.
    I'll make a determined effort to look tomorrow (Tuesday)

  10. #10
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Trouble shoot Daikin Controller

    Quote Originally Posted by frank View Post
    Unfortunately not. Had several things going on today which were unexpected.
    I'll make a determined effort to look tomorrow (Tuesday)
    Well then I still have something to look forward to. Many thanks.

  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Trouble shoot Daikin Controller

    Setting 44 in the Service mode can be used to set the airflow direction and fan speed for individual fan coils when using Group Control.

    Once you have made your settings you must use the Confirmation button to write the changes to memory.

    Have you addressed the fan coils with Group numbers?

    Did you Confirm the settings?

  12. #12
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Trouble shoot Daikin Controller

    Quote Originally Posted by frank View Post
    Setting 44 in the Service mode can be used to set the airflow direction and fan speed for individual fan coils when using Group Control.

    Once you have made your settings you must use the Confirmation button to write the changes to memory.

    Have you addressed the fan coils with Group numbers?

    Did you Confirm the settings?
    frank, I have four (4) FXSQ indoor units all controlled by a single BRC wired controller. No group numbers to set. When attempting to set fan speed of individual indoor units the fan speed selection button does not change the fan speed showing on the controller between 1 and 3 as it is supposed to do. So, the confirmation step is never reached. Similarly, when attempting to set the fan speed for all indoor units by using the fan speed button in any of the operating modes, the speed shown on the controller screen (large blades or small blades) will change but the actual speed of the indoor units does not change. Before I go for a new controller I hoped there was some way to confirm it is the controller that is misbehaving. This system is a couple of years old and all worked well when new. Thank you.

  13. #13
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Trouble shoot Daikin Controller

    You need to set each indoor fan coil with a group address so that the controller can define which one it is talking to. As you have a VRV-S system this is easy to do

    FCU1 = 1:00
    FCU2 = 1:01
    FCU3 = 1:02
    FCU4 = 1:03

    Group numbers are usually only set when using a centralised controller.

    Not all options are available for all indoor unit types. See the service manual for a list.

  14. #14
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Trouble shoot Daikin Controller

    Quote Originally Posted by frank View Post
    You need to set each indoor fan coil with a group address so that the controller can define which one it is talking to. As you have a VRV-S system this is easy to do

    FCU1 = 1:00
    FCU2 = 1:01
    FCU3 = 1:02
    FCU4 = 1:03

    Group numbers are usually only set when using a centralised controller.

    Not all options are available for all indoor unit types. See the service manual for a list.
    I don't have a centralized controller only the single remote. Each indoor unit has a unit number 00 thru 03 but no set group number. Each unit number appears in the controller and all other individual control is available. I can reassign unit numbers, force fan on for each individual unit using service code 43, and monitor temps in service code 41. But no fan speed selection, no how it is attempted.

  15. #15
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Trouble shoot Daikin Controller

    Those fan coil reference numbers that you see are allocated automatically by the self addressing system - they are not Group numbers.

    The service level 44 setting will/may only work if you manually address the indoor fan coils with a Group number. As I said, not all indoor unit types have the facility.

    Is there any information regarding setting Group numbers in your booklet?

    As you can see from the attached page, code 13,5 (02) needs an Optional Accessory to adjust the fan speed away from Standard and on Page 86, the wall unit FXAQ does not allow fan speed settings
    Attached Files Attached Files

  16. #16
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Trouble shoot Daikin Controller

    Quote Originally Posted by frank View Post
    Those fan coil reference numbers that you see are allocated automatically by the self addressing system - they are not Group numbers.

    The service level 44 setting will/may only work if you manually address the indoor fan coils with a Group number. As I said, not all indoor unit types have the facility.

    Is there any information regarding setting Group numbers in your booklet?

    As you can see from the attached page, code 13,5 (02) needs an Optional Accessory to adjust the fan speed away from Standard and on Page 86, the wall unit FXAQ does not allow fan speed settings
    frank, Thank you for this information. I do not remember anything on setting group numbers in my documentation, but will look specifically for that to make sure. I see what you say about the FXAQ not allowing fan speed selection and it shows the same for my units FXSQ. But, I used to be able to make the fan speed selection not only for all four indoor units at once by using the fan speed selection button on the controller, but also by service code 44. I have one unit now that is in low fan while the other three are in high fan as I had set that unit in low fan last summer. The point is something has changed where I could set the fan speed and now can not. For code 13,5(2) it is my understand that code is to set fan speed on additional equipment such as ventilator.

Similar Threads

  1. Daikin twin split trouble
    By dave ldms in forum Air Conditioning
    Replies: 1
    Last Post: 25-02-2010, 06:34 PM
  2. Daikin Residential Central Controller
    By mchild in forum Air Conditioning
    Replies: 2
    Last Post: 13-12-2009, 09:31 PM
  3. Daikin controller
    By mchild in forum Air Conditioning
    Replies: 8
    Last Post: 02-10-2009, 07:14 PM
  4. Daikin VRV-S controller configuration
    By mchild in forum Air Conditioning
    Replies: 1
    Last Post: 12-03-2009, 08:06 PM
  5. Daikin Controller
    By mchild in forum Air Conditioning
    Replies: 11
    Last Post: 24-11-2008, 02:34 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •