    Checking subcooling and superheat?



    Ok so ya checking subcooling and super heat is a great method of determining several things BUT how do I know my system needs 10degrees of subcooling, 8 degrees of subcooling, or even 20degrees of subcooling as all systems are different.

    My question is how do you know "the sweet spot" (subcooling) for each individual system?



  2. #2
    Join Date
    May 2010
    Location
    Dallas
    Age
    39
    Posts
    41
    Rep Power
    0

    Re: Checking subcooling and superheat?

    Any takers? anyone anyone... Bueller?

  3. #3
    Join Date
    Apr 2010
    Location
    USA
    Posts
    62
    Rep Power
    15

    Re: Checking subcooling and superheat?

    Quote Originally Posted by ZeroTolerance View Post
    Any takers? anyone anyone... Bueller?
    http://prostores1.carrierzone.com/se...com/StoreFront

  4. #4
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Checking subcooling and superheat?

    Quote Originally Posted by ZeroTolerance View Post
    My question is how do you know "the sweet spot" (subcooling) for each individual system?
    This is a very valid question. The real truth of the matter is - you will never know - unless you designed the system, or have tested it thoroughly.

    Each system will balance out differently depending on the components & piping used in the circuit. There will be a few basic rules in regards to superheat & subcooling:

    1. SH has a lower limit where control of the TXV becomes difficult;
    2. SH has an upper limit where the compressor discharge temp becomes too high;
    3. SC has a lower limit of 0K;
    4. SC upper limit will depend on the condenser type & liquid line piping;
    5. Allowing SC to become too large will push up Tc,sat (high-pressure);
    6. SC may rise, or fall over the range of an operating cycle, depending on the condenser & liquid line piping;
    7. The liquid sub-cooling at TXV inlet has a lower limit under which it is accepted that too much flash vapour could enter the TXV.

    Other posters may want to add to this list & insert the 'norms' of the RHVAC industry. I have particular views on these, based on my own system designs, which may differ to more seasoned veterans of the trade.
    Last edited by desA; 06-06-2010 at 05:31 AM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  5. #5
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Checking subcooling and superheat?

    Correct charging a refrigeration system is always achieved by measuring the sub cooling super heat.
    However the basis of sub cooling and Superheat for which is designed need to be known.

  6. #6
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Checking subcooling and superheat?

    ^ The problem is that, very often, I'll bet that the original system designer will not have a real idea of where the sweet-spot is at any particular point in the operating range.

    This sweet-spot varies over the heating range of a heat-pump, for instance. A similar effect will be seen for an a/c unit.

    I believe that it is a comfortable myth to think that there is a perfect arrangement for each RHVAC system. In my view, there are a number of suitable setup points for each system. Most system maintainers simply do not have the time to find the sweet-spot - they have to rely on rules-of-thumb & then pat themselves on the back when they land inside those. Who knows what happens at other operating points?

    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Checking subcooling and superheat?

    My rule of thumb is to keep subcooling higher than the temperature difference corresponding to the pressure drop across the liquid line. E.g. measure the pressure at condenser outlet, and convert to corresponding temperature. Do the same at the TXV inlet and convert to corresponding temperature. Subtract the two and find the deltaT corresponding to the pressure drop.
    That is your minimum subcooling.

    For the superheating, I generally keep it 1.5 times the glide of the refrigerant. If the refrigerant is azeotropic, then my minimum is 3K.

Similar Threads

  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Replies: 39
    Last Post: 19-07-2011, 03:16 AM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  3. subcooling and superheat are standard measurement or not?
    By karl2009 in forum Technical Discussions
    Replies: 3
    Last Post: 10-01-2009, 11:39 PM
  4. Replies: 12
    Last Post: 14-07-2008, 03:00 PM
  5. Superheat and subcooling
    By marc5180 in forum Training
    Replies: 27
    Last Post: 08-10-2007, 09:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •