    Pump down system, solenoid valve



    Hello guys!
    As you may see from my age, I'm pretty new to refrigeration, but I feel that I have a good understanding of the basics

    My question is as following:

    I have mounted a pump down system with two "freezer rooms" (not sure if "freezer rooms" is the right way to say it) at school. I have only runned it a few times.
    I have a Danfoss "EKC 204a" for each room.
    I have programmed -22 degrees celsius, as the setpoint. I know that the solenoid valve will close when I start a "defrost". The thing that I'am not 100% sure about is:

    Does the solenoid valve close when i reach -22 degrees celsius witch is my setpoint?

    Thanks in advance!

    Aleksander



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Pump down system, solenoid valve

    If you want to run it on pump down then yes the solenoid should be turned off when the room reaches -22C

    Jon

  3. #3
    Join Date
    Nov 2009
    Location
    Tromsoe, Norway
    Age
    31
    Posts
    10
    Rep Power
    0

    Re: Pump down system, solenoid valve

    Allright!
    Thank you very much

  4. #4
    Join Date
    Nov 2009
    Location
    Tromsoe, Norway
    Age
    31
    Posts
    10
    Rep Power
    0

    Re: Pump down system, solenoid valve

    Thought so, because when I ran the system I observed that when it reached -22C in one of the rooms I heard a "click" and the temperature reached about -22,5C. Then it started increasing all the way up to -18C. when it reached -18C it started dropping down to -22C again.

    Love the feeling off understanding things, and how they work

  5. #5
    Join Date
    Aug 2009
    Location
    england
    Posts
    85
    Rep Power
    15

    Re: Pump down system, solenoid valve

    Quote Originally Posted by monkey spanners View Post
    If you want to run it on pump down then yes the solenoid should be turned off when the room reaches -22C

    Jon
    true , set the L.P. switch up properly and you .ll be fine

  6. #6
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    894
    Rep Power
    19

    Re: Pump down system, solenoid valve

    Hi there,

    When pumping down the evaporator is starved and the suction pressure goes down so does the evaporating temperature.
    When this happened then your room temperature falls below thermostat setting. The bigger the evaporator the bigger is the temperature difference.
    In one application I had 3°C temperature fall when pumping down.

    Cheers
    Even Einstein Asked Questions

  7. #7
    Join Date
    Feb 2010
    Location
    Ireland
    Age
    38
    Posts
    82
    Rep Power
    15

    Re: Pump down system, solenoid valve

    Hi

    yes the valve closes as this is how your system controls it's self at your set point. Once it is reached the valve closes and the system pumps down. It then cuts the compressor out when it pumps down enough to activate the l/p switch. Then once the temp rises enough it opens the valve again it closes the l/p switch which is auto reset and the compressor starts again.


    Stick with it. It's a bad day when u don't learn something new.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 11:09 PM
  2. Lg mps system ( expansion valve location)
    By hussain2002cab in forum Air Conditioning
    Replies: 6
    Last Post: 18-03-2010, 11:19 PM
  3. Domestic Heat Pump System
    By jameswilson in forum Heat Pumps
    Replies: 27
    Last Post: 04-01-2010, 09:36 AM
  4. no reciever no solenoid valve chilling system
    By Yuri B. in forum Fundamentals
    Replies: 5
    Last Post: 15-06-2009, 03:21 PM
  5. System Pump Down
    By Brian_UK in forum Technical Speculations
    Replies: 16
    Last Post: 25-10-2001, 10:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •