    Pressure differential valve selecting



    How do you select pressure differential valve?
    For example it's Danfoss NRD, Sporlan ORD...
    Danfoss don't say the calculation of determine quantity of NRD.
    Sporlan gives:
    In those cases where the ORI-10 is applied on systems with more capacity than the ORD-4
    or when more than one head pressure control valve is
    used, it is necessary to use two or more ORD-4 valves in parallel.
    Could anybody explane how do you determine quantity of pressure differential valve in system with pressure regulating?


    In some places will have to think ...

  2. #2
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Pressure differential valve selecting

    Danfoss pressure regulator KVR may install on liquid pipe after condencer or on discharge pipe before condencer. Sporlan pressure regulator ORI may install only after condencer...
    Therefore I think there is two variants of calculating how much pressure differential valves are need...
    Does anybody know calculating method when two, three or more pressure differentials need in system? Or may be are there any ideas about it?
    In some places will have to think ...

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Pressure differential valve selecting

    I've never fitted any, so don't know

    Jon

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Pressure differential valve selecting

    From the little that I have read, Sporlan, you size the valve(s) on the duty duty and set the pressure at your required condensing temperature.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Pressure differential valve selecting

    I have come across large chiller systems 200Kw plus and the balance line is 1/2 " and an ord vav. Larger ammonia systems, no ord just a balance line from discharge straight onto receiver, below condenser of course.

  6. #6
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Pressure differential valve selecting

    I'm very surprised that you don't use it...
    http://www.danfoss.com/BusinessAreas...f6e172329.html
    In some places will have to think ...

Similar Threads

  1. discharge pressure relife valve opening
    By govindarajan in forum Trouble Shooting
    Replies: 10
    Last Post: 05-05-2010, 11:26 AM
  2. Relief Valve Sizing
    By GBRD in forum Industrial
    Replies: 6
    Last Post: 16-04-2010, 04:00 AM
  3. Pressure differential across air conditioned rooms
    By Rabindra in forum Air Conditioning
    Replies: 9
    Last Post: 25-10-2007, 09:30 AM
  4. Back Pressure Valve
    By guapo in forum Industrial Compressors
    Replies: 2
    Last Post: 18-03-2006, 05:38 PM
  5. Pressure, Vacuum and Differential
    By HVACGod in forum Air Conditioning
    Replies: 0
    Last Post: 01-11-2005, 04:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •