    Controlling a compressor off suction line temp, or pressure



    Scenario:
    1. RHVAC system operates in a hot country, say at T,ambient = 30'C;
    2. Trip compressor on suction line temp of 25'C;
    3. Want system to stay off for preset time;
    4. After time, system to re-start, run & pull suction temp down to below trip temp.

    Problems:
    a. If normal direct action controller is used, it will not re-start, since final temp above trip temp;

    How to manage this situation as inexpensively as possible?


    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Controlling a compressor off suction line temp, or pressure

    Quote Originally Posted by desA View Post

    How to manage this situation as inexpensively as possible?
    Push the compressor contactor with your index finger, until suction temp drops below trip temperature, then leave.
    Cost = 0 krugerrand.

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Controlling a compressor off suction line temp, or pressure

    Mmhhh... LOL.

    I meant as a permanent control strategy - perhaps using a Carel-type controller. Has me a bit flumoxed.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  4. #4
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Controlling a compressor off suction line temp, or pressure

    Wire start/start delay & off delay timer in parralell with suction trip device so that it energises on suction trip.

    When suction trip device returns to normal off delay timer energised to avoid momentary loss of control circuit power..

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Controlling a compressor off suction line temp, or pressure

    Yes, normally closed contact with delay on opening, just like gingerair said.

  6. #6
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Controlling a compressor off suction line temp, or pressure

    yes this situation was common < in the old days< pre-1960s most fridge units did not have stats they were controled off the L-p switch so when the evap went below the desiered temp off on L-p setting up was time consuming but in them days for a pound you could get 8 pints of beer land sea + air < fish chips + peas <
    and a taxi home, the good old days.

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Controlling a compressor off suction line temp, or pressure

    Quote Originally Posted by sedgy View Post
    yes this situation was common < in the old days< pre-1960s most fridge units did not have stats they were controled off the L-p switch so when the evap went below the desiered temp off on L-p setting up was time consuming but in them days for a pound you could get 8 pints of beer land sea + air < fish chips + peas <
    and a taxi home, the good old days.
    Have seen a few old milk tanks (alfa laval mostly) that regulated the ice bank on the lp switch, worked surprisingly well.

  8. #8
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Controlling a compressor off suction line temp, or pressure

    Quote Originally Posted by Gingerair View Post
    Wire start/start delay & off delay timer in parralell with suction trip device so that it energises on suction trip.

    When suction trip device returns to normal off delay timer energised to avoid momentary loss of control circuit power..
    Thanks so much for your input, Gingeair. Very much appreciated.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  9. #9
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Controlling a compressor off suction line temp, or pressure

    Quote Originally Posted by NoNickName View Post
    Yes, normally closed contact with delay on opening, just like gingerair said.
    Thanks very much 'NoNickName'.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  10. #10
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Controlling a compressor off suction line temp, or pressure

    Quote Originally Posted by desA View Post
    Scenario:
    3. Want system to stay off for preset time;
    4. After time, system to re-start, run & pull suction temp down to below trip temp.
    3. How long?

    4. If the units are running high SST, how would restarting them pull the SST down? Will the load change?
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

  11. #11
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Controlling a compressor off suction line temp, or pressure

    @ powell:

    Some very valid questions. The idea is to guard against a certain combination of load & ambient conditions which pushes suction line temp (!not SST!) above a certain threshold.

    The system should re-activate after an allowed off-time. If combined conditions again push the suction line temp over the limit, then stop again.

    Practically, this strategy could be improved with a number of additional features eg. lockout after so many re-starts, manual re-set etc.

    For the systems I work with, the load can most definitely change in the off-time, so again - it is the combination of load & ambient acting on affecting suction line temp.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  12. #12
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Controlling a compressor off suction line temp, or pressure

    desA,

    Actually a 30C (86F) ambient is not that hot. We see 43C (110F) plus here in Nevada all the time. Most refrigeration system units work well.

    Are you dealing with a system thats undersized, extra low temp (maybe R22), has possible control problems etc.?

    What type of system do you have?

    I would address the high superheat / overheating problem and cure the cause.
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

  13. #13
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Controlling a compressor off suction line temp, or pressure

    Quote Originally Posted by powell View Post
    desA,
    Actually a 30C (86F) ambient is not that hot. We see 43C (110F) plus here in Nevada all the time. Most refrigeration system units work well.
    Are you dealing with a system thats undersized, extra low temp (maybe R22), has possible control problems etc.?
    What type of system do you have?
    I would address the high superheat / overheating problem and cure the cause.
    Let's say the system is designed to run with high condensing temperatures. As such, this tends to pull up Te,sat & suction temp in sympathy - this is a byproduct of the particular technology. The system runs just fine, as designed. I'm working through a particular control strategy - trying to keep it as simple as possible.

    Actually, in my region, we often go over 42'C, at RH 72-75%. The 30'C was a typical value found in let's say, more moderate climates.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  14. #14
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Controlling a compressor off suction line temp, or pressure

    hi all is this thread an advert for holidays ?

Similar Threads

  1. what is useful of Economizer?
    By Ahmed.ragab in forum Industrial Compressors
    Replies: 33
    Last Post: 18-08-2010, 12:15 PM
  2. Suction line?
    By SkyWalker in forum Fundamentals
    Replies: 6
    Last Post: 18-05-2009, 10:34 PM
  3. High Liquid Line Temperature
    By airefresco in forum Commercial
    Replies: 37
    Last Post: 11-02-2009, 04:36 PM
  4. Supermarket suction line frosting
    By mccoolair@yahoo in forum Commercial
    Replies: 7
    Last Post: 14-02-2008, 11:53 PM
  5. Minimal required R134a speed in suction line
    By DaBit in forum CPU Overclockers
    Replies: 32
    Last Post: 08-05-2002, 05:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •