    C/R load, Equip Selection, Commercial sales



    In these hard times, refrigeration cold/freezer rooms is not just about best engineering, it about achieving sales with a high level of reliability.
    I see that there are plenty who want to know how to size and select equipment.
    So here goes.
    I am not going into specifics, as there is plenty of info available. (Software, but remember these programs are only as good as the information you feed it)
    With general purpose rooms the heat load is normally based on a total load per 24 hours then divided by a specified run time of the refrigeration unit.
    example; duty per 24hrs=240Kw
    refrigeration run time= 18hrs
    refrigeration duty = 13.33Kw.
    In the good old days run time was normally 16Hrs, but this can be stretched to 20hrs (as lonh as other point are followed)
    But how was the the daily duty calculated?
    Well if you are doing this job you should know the very basics.
    So lets look at air infiltration and wall transmission.
    What temperature do you use?
    Most use a very high figure, in NZ designers use 32C, we do get 32C (rarely) but we certainly do not get 24hours a day. Using this figure will only increase the design duty (thus oversizing the equipment required)
    A more realist design temperature is 26C (still higher than the 24hr daily averages).
    There are a number who do use this lower figure, and do achieve a high number sales, but they also have a significant amount of problems.
    WHY, the software programs that they use are normally generated by equipment suppliers, and all input data is directly used to select their equipment.
    So going back to our ambient which do you choose,
    32C grossly oversized, and over priced, or 26C smaller equipment but struggles when the ambient is high. NON
    Yes use the 26C for the room load, because this is a true real figure. "KW rating"
    But when it comes to the equipment selection, use the duty "KW rating" but selection this duty based upon the 32C ambient, not the 26C ambient.
    By now you should be asking why!
    If you did select the equipment at 26C and the ambient does rise to 32C (which it does) the capacity of the equipment reduces and is unable to recover quickly enough to ensure a reasonable level of temperture control "an unhappy client" and is likley to be adding undue stress on the equipment.
    If you select only at 32C your equipment will be grossly oversized, over priced, could short cycle, and you are unlikely to get the sale due to the price. (and that does become a waste of your time and money)
    In life we are now trained to look at products and services that are priced mid range.
    Cheapest are cutting corners
    Most expensive are screwing you.
    Those in the middle are offering a fair product for a fair price.
    With the above design method that is actaually were you will be and you can be confident that what you have installed will reliable and efficient.
    Of course you need specific desihn figure for each part of the world that you are in



  2. #2
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: C/R load, Equip Selection, Commercial sales

    So going back to our ambient which do you choose,
    32C grossly oversized, and over priced, or 26C smaller equipment but struggles when the ambient is high.
    You may select equipment at 32C ambient temperature and calculating refrigeration run time no more 22hrs. Real time of eqipment work will not be 22 hours, because ambient temperature of 32C will not be 24 hours per day.
    In some places will have to think ...

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: C/R load, Equip Selection, Commercial sales

    What multiyear middle temperature you will use here:

    Gray one is multiyear middle temperature
    Light blue is multiyear midle temperature decreased for one deviation.
    Blue is multiyear middle temperature decreased for two deviations.
    Light red is multiyear middle temperature increased for one deviation.
    Red is multiyear middle temperature increased for two deviations.
    Black one is this year middle temperature.

    Last edited by nike123; 05-06-2010 at 08:01 AM.

  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: C/R load, Equip Selection, Commercial sales

    Hi Nike,
    You need to zoom in to daily averages in summer (average daily temp for heat load calculation) maximum temp for equipment selection.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: C/R load, Equip Selection, Commercial sales

    Quote Originally Posted by mad fridgie View Post
    Hi Nike,
    You need to zoom in to daily averages in summer (average daily temp for heat load calculation) maximum temp for equipment selection.
    OK, here it is 27°C, but would you consider deviations or not? We get here sometimes 41°C or 42°C. It is 15K difference from daily average temperatures.
    Last edited by nike123; 05-06-2010 at 08:32 AM.

  6. #6
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: C/R load, Equip Selection, Commercial sales

    Whats is 27C is this your maximum daily temp.

  7. #7
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: C/R load, Equip Selection, Commercial sales

    In NZ the air temp is under 26C 99% of the time, therefore it is over 26C 1% of the time. Practically this means that the temp is above 26C for about 4 hours a day in the height summer

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: C/R load, Equip Selection, Commercial sales

    Quote Originally Posted by mad fridgie View Post
    Whats is 27C is this your maximum daily temp.
    Maximum daily average temperature for hottest day in October (hottest month in year)!

  9. #9
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: C/R load, Equip Selection, Commercial sales

    Quote Originally Posted by nike123 View Post
    Maximum daily average temperature for hottest day in October (hottest month in year)!
    So it would be fair to say that your maximum temperature is some what hotter than this.
    Is the 27C average over a 24hour period or over a lesser period (normal work hours for example)
    So at what temperature do you design coolrooms duty in your neck of the woods and do you select the equipment at the same temperature

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: C/R load, Equip Selection, Commercial sales

    Quote Originally Posted by mad fridgie View Post
    So it would be fair to say that your maximum temperature is some what hotter than this.
    Yes!

    Is the 27C average over a 24hour period or over a lesser period (normal work hours for example)
    Over 24 hours period.

    So at what temperature do you design coolrooms duty in your neck of the woods and do you select the equipment at the same temperature

    Usually at 32°C and 18hr system run time. I select equipment also at 32°C temperature. My calculation tool is CalcRite software. And my quotes are rarely accepted. Therefore I think I need to reconsider my calculations.
    Although, these rare customers that accept my quotes are usually happy with their cold rooms.

  11. #11
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: C/R load, Equip Selection, Commercial sales

    Ah yes, an over sized well balanced system very rarely causes problems but is more expensive.
    I would therefore size your load for 27C and 20 hours run time, but the equipment at 32C.
    Have ago on one of the system you lost, and see what differnce it would make to your price. Let us all know
    "Mad"

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: C/R load, Equip Selection, Commercial sales

    Quote Originally Posted by mad fridgie View Post
    Ah yes, an over sized well balanced system very rarely causes problems but is more expensive.
    I would therefore size your load for 27C and 20 hours run time, but the equipment at 32C.
    Have ago on one of the system you lost, and see what differnce it would make to your price. Let us all know
    "Mad"
    Ok, I will give result when I do that.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: C/R load, Equip Selection, Commercial sales

    I made some imaginary calculation.
    This one is you suggest:



    This one is as I would do it:



    Difference in capacity for this example is significant and it could lead to more acceptable quote for my customer.

  14. #14
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: C/R load, Equip Selection, Commercial sales

    Nice Nike, but still very reliable!

Similar Threads

  1. Heat Load Selection for EOT Cabin A/C in Steel Plants
    By Samarjit Sen in forum Tools and Calculators
    Replies: 12
    Last Post: 19-11-2010, 12:17 PM
  2. Blast Freezer Heat Load calculations
    By smpsmp45 in forum NH3
    Replies: 5
    Last Post: 03-04-2010, 10:20 PM
  3. Replies: 6
    Last Post: 19-01-2009, 06:35 PM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •