05-06-2010, 12:47 AM #1
"top up" R410
Hi guys,
whats the process you guys use on a new installation when you need to add extra 410 to the system, obviously without wasting the gas.
-
05-06-2010, 07:26 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: "top up" R410
Top up in liquid after vacuuming system and then open isolation valves. Start unit in heating test mode.
-
05-06-2010, 07:42 AM #3
Re: "top up" R410
add liquid under vacuum the open liquid (expansion line) first then suction run unit in heating first
-
05-06-2010, 02:38 PM #4
Re: "top up" R410
hey guys, thanks for your replies, bt, isnt there a way to top up with out vacuming, since its a new installation with extra pipping leght. ?
cumps.
-
05-06-2010, 03:35 PM #5
Re: "top up" R410
hi kad , I think what the other 2 replys where meaning is that , firstly, you should use a vac pump< after pressure testing< + what do you mean by extra piping on a new system
+ what dose waisting gas mean?
-
06-06-2010, 12:18 AM #6
Re: "top up" R410
hi again,
i think i'll need to explain this better as well as i can since english its not my "natural" language hehehe.
New AC unit, r410a, original charge up to 7 mts. the installation has a total of 15mts, obviously more ***** is necessary but the machine has no "charge point" on the liquid line, so, in this case how do you guys proceed? Vaccum all the system, leak test and charge all the system again ?
Is there anyway to make things easier\faster?
Im asking this because unfortunly the "tools" i have only allow me to collect the gas 4 recycling when in this case i only need a few grs. added to the system.
i hope i could make any sence now.
cumps.
-
06-06-2010, 11:20 AM #7
Re: "top up" R410
hi kad , you could add liquid into the suction< slowly< throttle the liquid valve to get this right, all the best
-
06-06-2010, 12:34 PM #8
Re: "top up" R410
If its a new install, pressure/leak test pipework. Vacuum pipe work. Charge pipe work with aditional charge needed for extra pipe work.
Then open the valves on the unit. Run up system.
-
06-06-2010, 01:27 PM #9
Re: "top up" R410
When system is running in cooling mode you can connect your manifold gauges to the access port on the suction service valve (large pipe).
Close off liquid line valve ( small pipe ) and when the suction pressure falls you can add the additional charge.
When you've finished adding refrigerant open the liquid line valve and your good to go.
Hope this is not an insult, but it seems to me this is what you wanted to know.
-
06-06-2010, 05:38 PM #10
Re: "top up" R410
hello again guys,
kiwireeferman - not insulted.
Thanks for all the replys.
-
07-06-2010, 08:35 PM #11
Re: "top up" R410
As has been stated you can run the system on cooling to introduce the extra gas you need, it is faster and easier to do this after you have vacced down the system (to 2 tor) after installation.
After reading the replies however I have a question. Why do you start the system up on heating first??
-
07-06-2010, 08:56 PM #12
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
07-06-2010, 09:31 PM #13
Re: "top up" R410
To keep compressor safe from liquid refrigerant.
__________________
Thanks
Similar Threads
-
Layman question re R410 tubing (xposting from Refrigerants)
By greekguy in forum Air ConditioningReplies: 6Last Post: 21-12-2010, 09:25 PM -
R410 Flaring
By daddymac in forum Air ConditioningReplies: 19Last Post: 22-10-2006, 05:57 PM -
want good price r410 flaring tool in aust ?
By peter1927 in forum Tools and CalculatorsReplies: 2Last Post: 24-11-2005, 05:48 AM -
R410
By Vincent Yu in forum FundamentalsReplies: 2Last Post: 19-10-2005, 01:10 AM