    Hi guys,
    whats the process you guys use on a new installation when you need to add extra 410 to the system, obviously without wasting the gas.
    Split Croatia
    6,151
    Re: "top up" R410
    Top up in liquid after vacuuming system and then open isolation valves. Start unit in heating test mode.
    Feb 2008
    502
    Re: "top up" R410
    add liquid under vacuum the open liquid (expansion line) first then suction run unit in heating first
    May 2010
    portugal
    44
    29
    Re: "top up" R410
    hey guys, thanks for your replies, bt, isnt there a way to top up with out vacuming, since its a new installation with extra pipping leght. ?
    cumps.
    Oct 2008
    mallorca, spain,
    75
    768
    Re: "top up" R410
    hi kad , I think what the other 2 replys where meaning is that , firstly, you should use a vac pump< after pressure testing< + what do you mean by extra piping on a new system
    + what dose waisting gas mean?
    May 2010
    portugal
    44
    29
    Re: "top up" R410
    hi again,
    i think i'll need to explain this better as well as i can since english its not my "natural" language hehehe.
    New AC unit, r410a, original charge up to 7 mts. the installation has a total of 15mts, obviously more ***** is necessary but the machine has no "charge point" on the liquid line, so, in this case how do you guys proceed? Vaccum all the system, leak test and charge all the system again ?
    Is there anyway to make things easier\faster?
    Im asking this because unfortunly the "tools" i have only allow me to collect the gas 4 recycling when in this case i only need a few grs. added to the system.
    i hope i could make any sence now.
    cumps.
    Oct 2008
    mallorca, spain,
    75
    768
    Re: "top up" R410
    hi kad , you could add liquid into the suction< slowly< throttle the liquid valve to get this right, all the best
    3,853
    Re: "top up" R410
    If its a new install, pressure/leak test pipework. Vacuum pipe work. Charge pipe work with aditional charge needed for extra pipe work.
    Then open the valves on the unit. Run up system.
    Jul 2006
    New Zealand
    77
    65
    Re: "top up" R410
    When system is running in cooling mode you can connect your manifold gauges to the access port on the suction service valve (large pipe).
    Close off liquid line valve ( small pipe ) and when the suction pressure falls you can add the additional charge.
    When you've finished adding refrigerant open the liquid line valve and your good to go.
    Hope this is not an insult, but it seems to me this is what you wanted to know.
    May 2010
    portugal
    44
    29
    Re: "top up" R410
    hello again guys,
    kiwireeferman - not insulted.
    Thanks for all the replys.
    Twin fan's Avatar
    Twin fan Guest
    Re: "top up" R410
    As has been stated you can run the system on cooling to introduce the extra gas you need, it is faster and easier to do this after you have vacced down the system (to 2 tor) after installation.
    After reading the replies however I have a question. Why do you start the system up on heating first??
    Split Croatia
    6,151
    Re: "top up" R410
    Quote Originally Posted by Twin fan View Post
    To keep compressor safe from liquid refrigerant.
    Twin fan's Avatar
    Twin fan Guest
    Re: "top up" R410
    __________________
  1. Layman question re R410 tubing (xposting from Refrigerants)
    By greekguy in forum Air Conditioning
    Last Post: 21-12-2010, 09:25 PM
  2. R410 Flaring
    By daddymac in forum Air Conditioning
    Last Post: 22-10-2006, 05:57 PM
  3. want good price r410 flaring tool in aust ?
    By peter1927 in forum Tools and Calculators
    Last Post: 24-11-2005, 05:48 AM
  4. R410
    By Vincent Yu in forum Fundamentals
    Last Post: 19-10-2005, 01:10 AM