    "top up" R410



    Hi guys,

    whats the process you guys use on a new installation when you need to add extra 410 to the system, obviously without wasting the gas.




  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: "top up" R410

    Top up in liquid after vacuuming system and then open isolation valves. Start unit in heating test mode.

  3. #3
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: "top up" R410

    add liquid under vacuum the open liquid (expansion line) first then suction run unit in heating first

  4. #4
    Join Date
    May 2010
    Location
    portugal
    Age
    44
    Posts
    29
    Rep Power
    0

    Re: "top up" R410

    hey guys, thanks for your replies, bt, isnt there a way to top up with out vacuming, since its a new installation with extra pipping leght. ?

    cumps.

  5. #5
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: "top up" R410

    hi kad , I think what the other 2 replys where meaning is that , firstly, you should use a vac pump< after pressure testing< + what do you mean by extra piping on a new system
    + what dose waisting gas mean?

  6. #6
    Join Date
    May 2010
    Location
    portugal
    Age
    44
    Posts
    29
    Rep Power
    0

    Re: "top up" R410

    hi again,

    i think i'll need to explain this better as well as i can since english its not my "natural" language hehehe.

    New AC unit, r410a, original charge up to 7 mts. the installation has a total of 15mts, obviously more ***** is necessary but the machine has no "charge point" on the liquid line, so, in this case how do you guys proceed? Vaccum all the system, leak test and charge all the system again ?

    Is there anyway to make things easier\faster?

    Im asking this because unfortunly the "tools" i have only allow me to collect the gas 4 recycling when in this case i only need a few grs. added to the system.

    i hope i could make any sence now.

    cumps.

  7. #7
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: "top up" R410

    hi kad , you could add liquid into the suction< slowly< throttle the liquid valve to get this right, all the best

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: "top up" R410

    If its a new install, pressure/leak test pipework. Vacuum pipe work. Charge pipe work with aditional charge needed for extra pipe work.
    Then open the valves on the unit. Run up system.

  9. #9
    Join Date
    Jul 2006
    Location
    New Zealand
    Age
    77
    Posts
    65
    Rep Power
    18

    Re: "top up" R410

    When system is running in cooling mode you can connect your manifold gauges to the access port on the suction service valve (large pipe).
    Close off liquid line valve ( small pipe ) and when the suction pressure falls you can add the additional charge.
    When you've finished adding refrigerant open the liquid line valve and your good to go.

    Hope this is not an insult, but it seems to me this is what you wanted to know.

  10. #10
    Join Date
    May 2010
    Location
    portugal
    Age
    44
    Posts
    29
    Rep Power
    0

    Re: "top up" R410

    hello again guys,

    kiwireeferman - not insulted.

    Thanks for all the replys.

  11. #11
    Twin fan's Avatar
    Twin fan Guest

    Re: "top up" R410

    As has been stated you can run the system on cooling to introduce the extra gas you need, it is faster and easier to do this after you have vacced down the system (to 2 tor) after installation.

    After reading the replies however I have a question. Why do you start the system up on heating first??

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: "top up" R410

    Quote Originally Posted by Twin fan View Post
    ading the replies however I have a question. Why do you start the system up on heating first??
    To keep compressor safe from liquid refrigerant.

  13. #13
    Twin fan's Avatar
    Twin fan Guest

    Re: "top up" R410

    To keep compressor safe from liquid refrigerant.
    __________________

    Thanks

Similar Threads

  1. Layman question re R410 tubing (xposting from Refrigerants)
    By greekguy in forum Air Conditioning
    Replies: 6
    Last Post: 21-12-2010, 09:25 PM
  2. R410 Flaring
    By daddymac in forum Air Conditioning
    Replies: 19
    Last Post: 22-10-2006, 05:57 PM
  3. want good price r410 flaring tool in aust ?
    By peter1927 in forum Tools and Calculators
    Replies: 2
    Last Post: 24-11-2005, 05:48 AM
  4. R410
    By Vincent Yu in forum Fundamentals
    Replies: 2
    Last Post: 19-10-2005, 01:10 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •