Thread: Mr. Slim MCB tripping problem
-
28-05-2010, 12:44 PM #1
Mr. Slim MCB tripping problem
Mitsuibishi make Mr. slim, Model :MU-A30VD,2.5 ton capacity,
MCB 2 pole 25 amp tripped within 2/3 minute after ac unit start.
I read the manual but not get the required information.
please guide the possible cause.
-
28-05-2010, 07:47 PM #2
Re: Mr. Slim MCB tripping problem
is this a new unit or old unit
-
28-05-2010, 08:09 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Mr. Slim MCB tripping problem
Measure amperage and see at what amperage MCB trips.
-
28-05-2010, 09:20 PM #4
Re: Mr. Slim MCB tripping problem
.. try it on fan only and see if it still trips. if it doesn't,.probably the compressor has gone
-
04-06-2010, 09:55 AM #5
Re: Mr. Slim MCB tripping problem
Thanks Multisync,
compressor has gone. it is rotary compressor.
can you guide, me the possible cause for this compressor failure.
where can I get information about troubleshotting /service manual for Mr Slim.
common thing we check electrical terminal,R22 gas pressure is 140 psi, voltage
Similar Threads
-
Aga freezer L245-R2 defrosting issues and RCD tripping
By SandyW in forum DomesticReplies: 5Last Post: 10-03-2011, 03:58 PM -
A strange problem
By MuhengineeR in forum Air ConditioningReplies: 14Last Post: 27-10-2010, 05:21 PM -
problem with a small cooler
By corvairbob in forum Trouble ShootingReplies: 1Last Post: 03-03-2010, 05:19 AM -
Water Pump Tripping Overload. (are you sitting comfortably)?
By Grizzly in forum ElectricalReplies: 14Last Post: 27-08-2008, 08:57 PM -
Mr Slim problem
By Andy AC in forum Air ConditioningReplies: 1Last Post: 12-02-2007, 10:21 PM