    Adjustable TXV



    I apologize for asking such a dumb question, but why would a manufacturer install a non-adjustable TXV on a brand new DX unit? There are hundreds of articles on superheat and how important it is to keep a system "Balanced". An HVAC system is no question going to lose efficiency over time for various reasons, but if your superheat is off the charts, isn't the best place to start making adjustments at the TXV? If you can't drop your superheat, then doesn't that signal to start looking in other places? Thanks for your input!



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Adjustable TXV

    The first law of refrigeration is - "Do not play with the TXV."

    Unless the TXV has gone faulty there is no reason to adjust the settings of the valve.

    There will be far more causes for poor performance such as airflow which should be checked first of all.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Nov 2006
    Location
    India
    Posts
    7
    Rep Power
    0

    Re: Adjustable TXV

    Non adjustable TXVs are used for standard applications were the load change is very minimal (airconditioners etc.,). For other applications it might be good idea to select adjustable TXVs. Even these are to be rarely adjusted in the field.

Similar Threads

  1. Compressor Overload setting
    By Chris2005 in forum Commercial
    Replies: 20
    Last Post: 23-06-2008, 03:20 PM
  2. Adjustable versus non-adjustable
    By Dan in forum Ye Old Wifes Tales
    Replies: 39
    Last Post: 03-12-2005, 10:41 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •