    RefComp can not start



    Hi we have onboard a ship a RefComp waterchiller.

    It is a RefComp SRC-S 305 (2 x screw compressors)

    We just made oil/filterchange on it and now we can not start again.

    We hav following alarms and we can not reset.

    48 L1 Probe fail
    48 L2 Probe fail
    48 H1 Probe fail
    48 H2 Probe fail

    While we were changing the oil/filters we had the power breaker off.

    Now after we put the breaker on we have these alarms.

    How can we get this Refcomp up and running again ?

    From Daniel....



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: RefComp can not start

    There is probably an alarm reset in the control panel, or you may have to access the maintenance program to allow you to reset these.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  3. #3
    Join Date
    Jul 2008
    Location
    UK
    Age
    60
    Posts
    94
    Rep Power
    16

    Re: RefComp can not start

    Quote Originally Posted by Challenger View Post
    Hi we have onboard a ship a RefComp waterchiller.

    It is a RefComp SRC-S 305 (2 x screw compressors)

    We just made oil/filterchange on it and now we can not start again.

    We hav following alarms and we can not reset.

    48 L1 Probe fail
    48 L2 Probe fail
    48 H1 Probe fail
    48 H2 Probe fail

    While we were changing the oil/filters we had the power breaker off.

    Now after we put the breaker on we have these alarms.

    How can we get this Refcomp up and running again ?

    From Daniel....

    The lp and hp transducers are not seeing any pressure, open the liquid solenoids briefly to get pressure up to 1 bar and alarm 48 should go.
    Last edited by ptsac; 03-06-2010 at 11:08 PM.

  4. #4
    Join Date
    Jun 2010
    Location
    Denmark
    Posts
    12
    Rep Power
    0

    Re: RefComp can not start

    I have it up and running now.

    It was impossible to manual reset these alarms. According to the manual the alarms has automatic reset.

    The suction and discharge valve was fully open, but i still had the alarms.

    Then i connected a small hose from the lubeoil filling valve to a service valve just before the thermostatic exp valve. I let in a little pressure to the compressure via the oil filling valve and then the alarms disappered.

    After that I was eable to start without any problems. Its running fine now..

    Bye bye.

    Daniel

  5. #5
    Join Date
    Jun 2010
    Location
    China
    Posts
    12
    Rep Power
    0

    RefComp RTH GRoup

    Here's a bit of history and contacts if you need them.

    RefComp and Thermokey form together the RTH group which is an independent group which has one owner who is the original founder Mr. Candio.
    RefComp makes the very same screw and piston compressors at their factories both near Vicenza in Italy and in Shanghai in China while Thermokey makes many types of heat exchangers for Air Con, Refrigeration , Process Control, Close Control , Power and Energy and Solar Energy markets and manufactures in Italy , China and Brazil.

    About 30 years ago Mr. Candio used to own Artec (heat exchangers) which he after sold to Alfa Laval. After RefComp was then founded and was a pioneering company with screw compressor technology specifically designed for HVAC and Refrigeration applications. During this past century Bitzer used to sell the large RefComp screw compressors through their sales network because back then they did not manufacture yet this kind of new screw compressor.
    After Thermokey was then founded. Nowdays Thermokey is pioneering in large aluminium microhannel heat exchangers specifically designed for HVAC and Refrigeration applications

    you can contact them at :

    sales@refcomp.it
    sales@thermokey.it

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Carrier 850 MT start problem
    By Maya in forum Transport
    Replies: 5
    Last Post: 18-05-2010, 10:49 PM
  3. Replies: 5
    Last Post: 08-11-2009, 05:10 PM
  4. Daikin VRV hot start control
    By mchild in forum Air Conditioning
    Replies: 0
    Last Post: 04-06-2009, 03:15 PM
  5. Hermetic analyzer " ANNIE" how do they work
    By kengineering in forum Tools and Calculators
    Replies: 11
    Last Post: 02-03-2008, 06:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •