    Trane actuator problems on centrifs



    Hi guys

    any one got any info on the actuators for Trane centrif compressors, i understand how they work (opening and closing internal veins inside the compressor) but i could do with some literature to assist with an ongoing issue
    I have 1 actuator that likes to stay fully open and 1 that likes to stay fully closed

    Trane model CVAD 32

    please can you email any literature to

    jack.keating@brooktherm.co.uk

    thanks again guys



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: Trane actuator problems on centrifs

    Hi, Check The internal reed type-end switches that determine when the actuator should open or close. The actuator will not open if the external end limit switch is not made, indicating that the vanes are in fact 100% shut on start up.
    Does the unit unload in Manual unload, if not then the internal connections on the actuator and winding resistances need to be checked. Good Luck

  3. #3
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    29
    Rep Power
    0

    Re: Trane actuator problems on centrifs

    yes it loads & unloads in manual, it also has rather high head pressure for 134a approx 12bar then it starts surging and dropping to about 9 bar for a few seconds
    i have taken a sample of the gas in a small dumpy reclaim bottle and after a while done a pressure to temp reading to check for non-condensables and all seems ok

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Trane actuator problems on centrifs

    Quote Originally Posted by sefuss View Post
    yes it loads & unloads in manual, it also has rather high head pressure for 134a approx 12bar then it starts surging and dropping to about 9 bar for a few seconds
    i have taken a sample of the gas in a small dumpy reclaim bottle and after a while done a pressure to temp reading to check for non-condensables and all seems ok
    Hi yep you are well above usual working pressure ,it would seem your condenser needs cleaning ,some of these units will not load if hi side is above a certain setting,
    lower your head pressure and it should be the remedy.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  5. #5
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: Trane actuator problems on centrifs

    Hi, There is a transducer in the UCM Panel ( 1/4 Mf Connection ) This is the Hp limit Protection device- Non Adjustable. As Goshen Says- check your condenser Approach Temperature. Should be less than 3 Deg at load. Good Luck

Similar Threads

  1. Trane chiller Training
    By sefuss in forum Training
    Replies: 0
    Last Post: 26-05-2010, 05:01 PM
  2. Trane CenTraVac
    By dr-energy in forum Commercial
    Replies: 1
    Last Post: 17-12-2009, 02:22 AM
  3. AEC Pinical chiller with trane comp
    By cptrdbrd in forum Commercial
    Replies: 1
    Last Post: 28-10-2009, 09:47 PM
  4. trane ertaa213 EEV fault (1AA)
    By knight rider in forum Technical Discussions
    Replies: 4
    Last Post: 11-06-2009, 06:40 AM
  5. Trane Defrost Control Board Energize "W" in cooling
    By jcmorris2 in forum Heat Pumps
    Replies: 6
    Last Post: 02-06-2007, 03:40 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •