    Hi All, Thanks in advance for any comments.

    Ive been having a friendly discussion with a A/C tech who is much my senior regarding a pair of condensors we are replacing on board a large sailing yacht that i work on. The question is regarding the cooling water flow through a water cooled shell and tube condensor, in our case salt water cooled. The condesor is a 2 pass on the water ( throught the tubes) side unit with hot gass entering from the top (through the shell) and cooler liquid out of the bottom. My question is does the water initialy enter at the top to contact the hot gas first or through the bottom to further cool the colder liquid refrigerant in the condensor.

    I belive the cold water should flow opisite to the direction of the gas/ liquid ie warm water before it exits contacts hottest gas and coldest water contacts coolest gas.

    He has 25 yrs + experience hence the reason im asking you guys and trying not to be a young punk know it all.

    thanks



  2. #2
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Water cooled condensor theory

    water enters at liquid out leaves gas in

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Water cooled condensor theory

    Opposite, always use counterflow and also to be sure you could remove the air out of the condenser.

    http://www.engineersedge.com/heat_ex...nger_types.htm
    http://www.engineersedge.com/heat_tr...ow_designs.htm
    http://en.wikipedia.org/wiki/Heat_exchanger
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Water cooled condensor theory

    cold to cold and hot to hot is general practice thus the cooling water enters bottom and leaves at top so that it cools /sub cool (normally additional tubes provided in many condensers design)the liquid and cool the high temperature gas to condense. Thus top is wher high temperature gas enters and the cooling water leaves to cooling tower

  5. #5
    adamcheng's Avatar
    adamcheng Guest

    Re: Water cooled condensor theory

    Thanks very much guys,

    I thought i was correct but as i said he has quite alot of experience and i didnt want to disagree with him.

Similar Threads

  1. reusing heated water from water cooled cond.
    By Richvacr in forum Technical Speculations
    Replies: 5
    Last Post: 11-02-2011, 10:55 PM
  2. VRV water cooled
    By thrustmaster22 in forum Fundamentals
    Replies: 0
    Last Post: 09-02-2010, 07:16 PM
  3. Problem with water cooled compressor
    By bksingh in forum Trouble Shooting
    Replies: 4
    Last Post: 15-05-2009, 01:04 PM
  4. water cooled subcooler?
    By star882 in forum Technical Speculations
    Replies: 1
    Last Post: 29-12-2007, 11:21 PM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •