    Cleaning tubes in Shell and tube condenser



    Does anyone know the procedure to clean the copper tubes of a shell and tube water cooled heat exchanger?
    what cleaning agents should I use?



  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Cleaning tubes in Shell and tube condenser

    Hi there,

    The cleaning agent is Hydrochloric Acid with 10% concentration.
    Commercial de-scaling agents usually contain corrosion inhibiting agents.
    Be careful, copper inhibiting agents are very corrosive with galvanized steel. Separate the copper pipework from the steel piping.
    You have to use a tank with a pump and circulate the solution through the condenser. When de-scaling is complete then circulate some kind of alkaline solution to neutralize the acid. After that circulate water to clean the remaining residue.
    Cheers
    Even Einstein Asked Questions

  3. #3
    Join Date
    May 2010
    Location
    Sri Lanka
    Age
    39
    Posts
    21
    Rep Power
    0

    Re: Cleaning tubes in Shell and tube condenser

    Thank you lana.

Similar Threads

  1. Replies: 2
    Last Post: 08-06-2010, 11:12 PM
  2. Chemical Cleaning on fouled tubes
    By jayaeros in forum Air Conditioning
    Replies: 1
    Last Post: 09-09-2009, 06:00 PM
  3. Fabrication of Cooler Tube & Shell Cooler
    By rickyccong in forum Technical Discussions
    Replies: 1
    Last Post: 27-07-2009, 02:25 PM
  4. Water velocity in Shell and tube HE
    By wilsoncheung in forum Industrial
    Replies: 15
    Last Post: 07-04-2009, 07:59 PM
  5. Replies: 3
    Last Post: 09-09-2008, 04:33 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •