    Apr 2006
    Northern Ireland
    31
    oil Return for R410a
    Would like to know what is the limit on the length of a vertical riser for the suction line, size 1.1/8 (Inch and one eighth) on a 410a installation. Capacity of system 12 kW, evaporating @ -5C, condensing @45C. What trapping arrangements is needed to insure proper oil return. All help appreciated.
    Aug 2009
    New Zealand
    2,554
    26
    Re: oil Return for R410a
    Quote Originally Posted by mac_J View Post
    I would say that your suction line is way to big for this duty, I would choose 3/4" and a trap every 3-4 meters
    Oct 2005
    IRAN
    878
    You did not mention the length of the pipe both horizontal and vertical.
    For 20 m run you need 7/8" suction tube. If you give exact number of fittings and length then I can give you the exact tube size.
    About the vertical riser : If you use correct pipe size then only you need oil traps. Depending on your tube size you have to install oil traps every few meters. For example for 7/8" tube every 5 m is OK. There is no formula to calculate the traps distance. The bigger the diameter then more oil is on the tube walls.
    Even Einstein Asked Questions
  1. daikin return air problem
    By Kev The Tool in forum Air Conditioning
    Last Post: 17-02-2010, 03:50 PM
  2. McQuay ALS F XE273.2 990Kw, highest return temp?
    By THE WOMBAT in forum Technical Speculations
    Last Post: 07-08-2009, 10:59 AM
  3. Best place for return air sensors, in the room or ceiling void?
    By back2space in forum Air Conditioning
    Last Post: 06-07-2009, 06:21 AM
  4. Oil return problems
    By Peter_1 in forum Industrial
    Last Post: 23-08-2004, 11:30 PM
  5. return air
    By subzero*psia in forum Air Conditioning
    Last Post: 12-07-2001, 04:02 PM