    Rotalock dillema



    I have one AC with two Rota-lock valves on hermetic compressor that has faulty HP/LP pressurestat.
    I need to change that HP/LP pressurestat.
    Its capillaries are connected at each rota-lock valves which have two ports. One port is near the stem of valve and other port is more in middle of valve. Capillaries are connected at that other port near middle of valve.



    From my memory this port cannot be closed by manipulating valve stem. It is always open to valve body.
    What is easiest way to change that HP/LP pressurestat without carrying vacuum pump and recovery cylinders.
    I need to do that job on some island and i wish to avoid excessive costs by transporting my van with ferry which is very expensive for me and my customer.



  2. #2
    Join Date
    Mar 2008
    Location
    England
    Posts
    232
    Rep Power
    20

    Re: Rotalock dillema

    Quote Originally Posted by nike123 View Post
    I have one AC with two Rota-lock valves on hermetic compressor that has faulty HP/LP pressurestat.
    I need to change that HP/LP pressurestat.
    Its capillaries are connected at each rota-lock valves which have two ports. One port is near the stem of valve and other port is more in middle of valve. Capillaries are connected at that other port near middle of valve.



    From my memory this port cannot be closed by manipulating valve stem. It is always open to valve body.
    What is easiest way to change that HP/LP pressurestat without carrying vacuum pump and recovery cylinders.
    I need to do that job on some island and i wish to avoid excessive costs by transporting my van with ferry which is very expensive for me and my customer.
    Well if it is not leaking why don't you leave the old one in place and fit a new one to the guage port, which you can access by back seating it and fit a Tee fitting so you will still have the guage access.
    Might not be the best asthetic result but it will avoid your costs.

  3. #3
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: Rotalock dillema

    Quote Originally Posted by nike123 View Post
    I have one AC with two Rota-lock valves on hermetic compressor that has faulty HP/LP pressurestat.
    I need to change that HP/LP pressurestat.
    Its capillaries are connected at each rota-lock valves which have two ports. One port is near the stem of valve and other port is more in middle of valve. Capillaries are connected at that other port near middle of valve.



    From my memory this port cannot be closed by manipulating valve stem. It is always open to valve body.
    What is easiest way to change that HP/LP pressurestat without carrying vacuum pump and recovery cylinders.
    I need to do that job on some island and i wish to avoid excessive costs by transporting my van with ferry which is very expensive for me and my customer.

    You are correct.

    So if you front seat the suction (wind it all the way in) and pump down the comp, then turn off the unit and front seat the discharge valve (again wind all the way in).

    You have now isolated the comp from the system and you can change the hp / lp parts with little or no loss.

    A quick vac of the comp will ensure it has no air inside (there will be little but a vac is best).

    All the best

    coolrunnings

    .

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Rotalock dillema

    Quote Originally Posted by B G Scott View Post
    Well if it is not leaking why don't you leave the old one in place and fit a new one to the guage port, which you can access by back seating it and fit a Tee fitting so you will still have the guage access.
    Might not be the best asthetic result but it will avoid your costs.
    That will be last option since old one is rusted and I am not confident that it will not leak soon.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Rotalock dillema

    Quote Originally Posted by cool runings View Post
    You are correct.

    So if you front seat the suction (wind it all the way in) and pump down the comp, then turn off the unit and front seat the discharge valve (again wind all the way in).

    You have now isolated the comp from the system and you can change the hp / lp parts with little or no loss.

    A quick vac of the comp will ensure it has no air inside (there will be little but a vac is best).

    All the best

    coolrunnings

    .
    Thanks, that was my preferred solution too.
    Vacuuming is no option so careful pump down with little overpressure in suction will resolve issue with air. Than same thing on high side will keep air from entering. I will probably use plastic capillaries that will help quicker switching and minimal loss of refrigerant.

  6. #6
    Join Date
    Mar 2008
    Location
    England
    Posts
    232
    Rep Power
    20

    Re: Rotalock dillema

    Quote Originally Posted by B G Scott View Post
    Well if it is not leaking why don't you leave the old one in place and fit a new one to the guage port, which you can access by back seating it and fit a Tee fitting so you will still have the guage access.
    Might not be the best asthetic result but it will avoid your costs.
    OK sorry about that but you did stress the financial issue more than the tech result.
    I see more good advice coming from memebers that is what the site is all about

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Rotalock dillema

    Quote Originally Posted by B G Scott View Post
    OK sorry about that but you did stress the financial issue more than the tech result.
    I see more good advice coming from memebers that is what the site is all about

    No need for apologies! Thanks for your input.

  8. #8
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Rotalock dillema

    sounds like you might as well bite the bullet now nike if the service valve is in bad repair.you could always walk onto the ferry with a wheelbarrow of tools and be picked up the other side
    enjoy your get away and dont forget the fishing rod
    mmm to beer or not to beer...........lets drink breakfast

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Rotalock dillema

    Fortunately, ten years ago, when I commissioned that AC, i used 1/4" copper pipe to connect HP/LP pressurestat to rota-lock ports. Solution is so easy and I have it in my tool bag! Just needed some time to mature in my head!

  10. #10
    Join Date
    May 2009
    Location
    aust
    Age
    53
    Posts
    12
    Rep Power
    0

    Re: Rotalock dillema

    I"ve been known to change the bellows if you can find the same pstat.

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Rotalock dillema

    Quote Originally Posted by lice to chill View Post
    I"ve been known to change the bellows if you can find the same pstat.
    Sorry, I don't understand! I have same pstat but contact group does not function as supposed. I don't like to go there more than one time and I want to do that in first attempt.

Similar Threads

  1. Leaking Rotalock
    By Grizzly in forum Industrial Compressors
    Replies: 4
    Last Post: 06-10-2009, 07:36 PM
  2. Rotolock or Rotalock
    By BESC5240 in forum Commercial
    Replies: 3
    Last Post: 14-11-2008, 08:15 PM
  3. Tightening rotalock valves
    By monkey spanners in forum Tools and Calculators
    Replies: 11
    Last Post: 02-09-2007, 06:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •