    Jun 2008
    Australia
    22
    2kW AC compressor high current.
    Hi all,
    what is a rough resistance on PSC 1Ph motor of about 2kW input power. I have 0.5ohm and 1.5ohm roughly. Is this in the ballpark? I compressor is pulling big amps (2x max running), it is a rotary type, starts OK but I am suspecting that the compressor is sticky. The only thing that doesnt make sense with that diagnosis is that a sticky compressor wouldn't start easily right? should i change out the capacitor?
    thank you!
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2008
    u.a.e
    49
    412
    23
    Re: 2kW AC compressor high current.
    Quote Originally Posted by Harrison View Post
    Hi all,
    thank you!
    what is you ampere and voltage?
    Jun 2008
    Australia
    22
    240V so that makes running amps 8.5A. I have been thinking a bit more, if a bad capacitor was causing the extra current (over double running amps, 21A or so) surely the cap would be getting seriously hot, no?
    thoughts??
    3,856
    You need to check the existing cap with a test meter to see if it is out of range.
    If you were to swap the cap and it worked ok, maybe the cap was bad, maybe it would have run ok that time anyway.
    The cap could be bad and the system could have another fault, a test meter will help you determine whats going on.
    Jon
    Jun 2008
    Australia
    22
    Ok Cap may be bad what do people think about the resistances in the motor windings. I know there are some reference books around with tech data for common compressors, where does one get these??
    thank you
  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Last Post: 23-01-2012, 11:23 PM
  2. Maximum Starting Current
    By weeliang82 in forum Air Conditioning
    Last Post: 29-04-2010, 04:15 AM
  3. Scroll compressor current
    By Scott Buker in forum New Technologies
    Last Post: 02-10-2009, 11:54 PM
  4. York Reciprocating Chiller - %Motor Current
    By subdude in forum Trouble Shooting
    Last Post: 28-07-2009, 05:49 PM
  5. Motor Current Fault York RecipPak YCUZ880E8
    By iaHVACguy in forum Trouble Shooting
    Last Post: 23-07-2009, 02:58 PM